Conditions for Paralleling Two or More Transformers

07/10/2012 3:00 PM

hello people can someone please fully explain to me the conditions that are required for paralleling 2 Txs ,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: conditions for paralleling two or more transformers

07/11/2012 3:19 AM

The voltage has to be the same, the frequency has to be the same and all phases have to be the same, for starters. Each tranny has to have its own protection arrangements for seconds, and a protocol for what happens if one of the two transformers goes off-line is the third requirement.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Conditions for Paralleling Two or More Transformers

07/11/2012 7:28 AM

To add to what PWSlack said, it is best for the transformers to be the same kVA rating and very close % impedance, or they will not share the load equally. If they are different ratings, they can't necessarily be expected to share the load proportionally, so it can cause problems with overloading/overheating.

If they have on-load tap changers (OLTC), there needs to be additional control circuitry for the OLTCs to work in parallel to prevent runaway tap changing, circulating currents, and uneven load sharing.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#3

Re: Conditions for Paralleling Two or More Transformers

07/11/2012 5:20 PM

The transformers to be connected in parallel to share the load proportional to their KVA ratings, the following conditions are required to fulfill.

1. Primary windings of the transformers should be suitable for the supply system voltage and frequency.

2. The transformers should be properly connected with regards to polarity.

3. The ratings of both primaries and secondaries should be identical. In other words, the transformers should have the same turn ratio i.e. transformation ratio.

4. The percentage impedances should be equal in magnitude and have the same X/R ration in order to avoid circulating currents in secondary loop formed by two transformers secondary windings. So they do not share load KVA in proportional to their KVA ratings. And causes more heating in the secondaries.

5. With transformers having different KVA ratings, the equivalent impedances should be inversely proportional to the individual KVA rating if circulating currents are to be avoided.

Generally paralleling of transformers is avoided to share the load. So the load is divided during the design stage such that each load can be fed by individual transformer. This solves a big problem that if one of the parallel transformers were fail it could not be found matching transformer to replace with new one especially having the same percentage impedance of the failed transformer

__________________
B.E, M.I.E, M.S
Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#4

Re: Conditions for Paralleling Two or More Transformers

07/13/2012 12:03 AM

Added to all the above replies vector group should be same.

For detailed information on transformer parallelling see the link below

http://seniordesign.engr.uidaho.edu/2008_2009/oltc/7400DB0701.pdf