What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/10/2012 9:58 PM

Please advise me for the model and brand of contactor to disconnect my generator from home distribution panel.

When the blackout happens I turn off the main breaker of the distribution panel and connect the 220V generator to the existing two phase copper bars(110V to neutral each). Turn on the generator. I got lights and the fridge functionality.Some time use PC.

When the net power is restored I must detach generator and turn on the distribution panel breaker.

Thinking how to avoid attaching/detaching generator's wires.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/11/2012 3:25 AM

Ideally it needs to be a changeover arrangement with a feed from either the mains or the generator, and not both, with the common connection to the house supply. It must be rated to carry the maximum supply current from the mains supply.

There are other ways of doing it depending on the rating of the generator and the detail of the house wiring, which cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
4
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#2

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/11/2012 5:18 AM

There are several ways to do this and make it much easier for you to make the transfer from the mains to the generator.

While your question asks about a contactor to use as a disconnect, in most locations this would be a serious code violation and is intrinsically unsafe so please don't use a contactor for this application. Even if you used a triple pole double throw electrically operated mechanically held contactor that could not backfeed the mains from your generator, you would still have to manually shut off all the circuits in your panel that you don't want powered by the generator.

What you need is a generator transfer switch and there are a variety of these for different applications based on generator size, load, number of circuits, indoor/outdoor, and many other considerations.

The simplest and best device to use is a commercially available Transfer Switch, which can be manual or automatic operation. These are readily available at Home Depot and Lowe's and almost any commercial electrical supply, Ace Hardware, Northern Tool, or any store that sells standby/backup generators.

Transfer Switches are made by Schneider/SquareD, GE, Kohler, Generac, Onan, etc. These transfer switches are made in a variety of sizes to accommodate small loads on a few circuits, up to large panels that will allow a typical residence (or even commercial facility) to run on very large standby equipment.

The smartest installation method is to hire a professional licensed electrician to install one of these transfer switches for you. If you are a competent electrician you should be able to follow the manufacturer's instructions included with the switch.

http://www2.northerntool.com/generators/transfer-switches-4.htm

http://www.electricgeneratorsdirect.com/power/manual-transfer-switches.html

http://www.gen-tran.com/

http://en.wikipedia.org/wiki/Transfer_switch

__________________
txmedic3338
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #2

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/12/2012 1:13 AM

Is using 2 nos 4P contactors with electrical and mechanical interlocks acceptable by codes?.

__________________
pnaban
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#13
In reply to #7

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/12/2012 11:26 AM

Each jurisdiction has its own set of codes. Ask your local authority not someone half way around the world.

__________________
Elnav
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#15
In reply to #7

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/13/2012 7:39 AM

Acceptable to code? Must be.

The arrangement you stated works fine (from experience) and eliminates the risk of having both connected together.

After all some "proper" ATS have this very arrangement at their core.

Sometimes just 3 pole common neutral.

Some ATS have motor driven switch.

OP could even use a 100% manual changeover switch and forget the contactors altogether.

Really depends on what OP needs, wants, or is capable of.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Jul 2012
Location: undisclosed location in N Atlantica
Posts: 32
#3

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/11/2012 5:57 AM

I totally agree with#2.Do it right.

Do not be responsible for killing someone working on a HV line presumed to be "OFF".

The transformer on the pole works both ways;It steps the voltage down from 13.2Kv to 240volts, but it will also work in reverse, if voltage is applied to the secondary when the primary is disconnected.So even though your generator only generates 240 volts, it will put 13.2Kv on the feeder line if not properly isolated.

Most localities also require a licensed electrician to install the transfer switch.

Although you may be allowed to wire your own house, or shop,(in effect, you can jump with the parachute that you packed), when someone else is at risk, you must be licensed.

__________________
eschew obfuscation, espouse elucidation
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#4
In reply to #3

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/11/2012 11:33 PM

I have had different thoughts as to whether the neutral should also be isolated with the generator changeover switch, ie should a two pole switch be used to isolate the incoming neutral or is single pole switch sufficient. In NZ jurisdiction either approach can be used. Any thoughts?

Either way a suitable qualified electrician should do the job.

I recently came across a faulty changeover switch installation where not only could the genset back feed the 11kV distribution line, but the pins on the plug for the genset to plug into the mains board were live when the switch was on "mains" mode.

Scary.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#5
In reply to #4

Re: What model contactor goes to disconnect my generator from home distr.panel?

07/11/2012 11:47 PM

The transfer switch should be double pole double throw type, so that both the phase and the neutral are isolated. There shouldn't be interconnection between the supply neutral and the generator neutral.

Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#6

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 12:26 AM

This is an inexpensive alternate way of doing the switchover: http://www.interlockkit.com/intro2.htm

It's an interlock kit for an existing panel that does not allow both breakers to be on simultaneously.

It's possible that the manufacturer of your panel has an interlock kit available for your panel.

Register to Reply
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#8
In reply to #6

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 1:36 AM

Is there equipotential bonding on that metal interlock?

The best way to put a changeover switch in is to build the board with a changeover switch in mind so that loads that are out side of the capability of the gen-set are not included in the circuits that are being powered up.

If your gen-set is less than 5kW (and remember that the manufacturers of those little petrol gen-sets are usually quite overly optimistic about the performance of their equipment) it is really good to have fridges, freezers, lights, domestic water pressure pumps, septic tank pumps etc separated from hobs, ovens, air-con.

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#9

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 3:34 AM

There are change over switches that need no intervention at all, they automatically isolate the mains coming in stat the Genny & switch to Genny,then when the power is restored it reverses the procedure. Its a long time since the last one I fitted so you need to trawl through some suppliers to find a switch, look under boat chandlers they supply a good range.

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 5:48 AM

"When you cannot afford to lose, don't gamble."

Do not trust ad-hoc engineering in a life or death situation.

Opinions do not matter in this case,unless from a qualified individual, and a truly qualified individual will not offer advice to an unlicensed individual for fear of potential liability issues in the future.

Use only UL approved transfer switch.

Be safe, or be sorry.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#11
In reply to #10

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 6:44 AM

I think the question is " What contactor not contractor", still who am I to stop you waxing lyrical on the subject.

Bazzer.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12
In reply to #11

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 7:03 AM

I think my answer(#10) gives a valid response to either question.

In reply to your interrogative:Nobody.

As for lyrics:

I'm a nobody,

Who are you?

Are you a nobody too?

Hush!

They'll banish us you know

Don't tell- they'll advertise

Oh how dreary to be somebody

So public, like a frog

To croak away the month of June

To an admiring bog.

(Emily Dickinson)

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#16
In reply to #10

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/15/2012 5:14 PM

I have to totally agree with you HiTek, I took some time off and I see that things are still cruising along the same here. It's great to help someone out in a areas that won't kill themselves or some poor fool lineman trying to scratch out a living on a pole that should be by all accounts be off line.

When you come to a forum such as CR4 asking a remedial question about what contactor to use for switch gear, tells me that this individual is not qualified to perform what they want to do. And any info. gleamed here, could potentially kill someone

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Commentator

Join Date: May 2011
Location: Brisbane, Australia
Posts: 62
Good Answers: 3
#14

Re: What Model Contractor Goes to Disconnect My Generator From Home Distr.Panel?

07/12/2012 5:47 PM

Sadly yet again the originator does not identify where s/he is from so while all advice is in the best interest of solving the issue, it may be completely wrong for the individuals situation. Unless we know what country you are in iaraktchiev no advice can be tailored specifically to suit the legislative requirements of your country rather we give advice based on our experience and/or home country.

While I could provide an exact solution to suit my home country I will not provide any advice to anyone without knowing where they are. All I will say is, with electricity, if you don't know then find someone qualified to do the job for you and avoid becoming yet another charred statistic.

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: