Power Transformer Current Density

07/11/2012 2:32 AM

We are purchasing a power transformer from a vendor. It's a Delta/Star, 66/11kv,10 MVA Power transformer. We have specified a current density of 2.8 A/Sq.mm

On Primary side, its delta connection.

As per our calculations:

Primary current = 10000/(1.732*66) = 87.47 A

Cross section of primary conductor is 22.62 Sq.mm (As per Vendor's Design. Data provided by vendor)

Current density = 87.47 / 22.62 = 3.86 A/Sq.mm. This exceeds the value specified by us.

All the above are as per our calculations.

As per the vendor,

The current 87.47 A is Line current on delta side. Hence the phase current (i.e., current actually flowing through the winding) will be 87.47/Sqrt(3) = 50.50 A

50.50 / 22.62 = 2.23 A/ Sq.mm (as per specifications)

What is correct? Please clarify.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Power Transformer Current Density

07/11/2012 2:43 AM

I think you are correct, and that the vendor is applying the 1/√3 factor twice.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 4)
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#2

Re: Power Transformer Current Density

07/11/2012 5:34 AM

if the primary were in Star config, than the vendor would be correct...

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #2

Re: Power Transformer Current Density

07/11/2012 7:49 AM

No, if the primary were in Star (Wye), then the line current = the phase current, which would be the 87.47A figure. With a delta winding, the current from each line connection splits between two windings each way, per the 1/√3 factor, and you get the 50.50A figure. I believe the transformer vendor is correct.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Power Transformer Current Density

07/11/2012 7:41 AM

May I ask why you are specifying the current density of the transformer's windings? That is usually a design element that the transformer manufacturer determines to give you the rating of transformer (MVA, %Z, physical size constraints, thermal ratings, etc.) that you request.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Associate

Join Date: Oct 2009
Posts: 26
Good Answers: 1
#7
In reply to #3

Re: Power Transformer Current Density

07/12/2012 1:10 AM

You are right and vendor info also correct

Register to Reply
2
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#5

Re: Power Transformer Current Density

07/11/2012 5:38 PM

The vendor's calculation is the correct one definitely

Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#6

Re: Power Transformer Current Density

07/11/2012 11:43 PM

Any time a transformer is changing voltage between three phase power, there is no sq rt 3 calculation between primary and secondary. It is always 3 phase and your initial calculation was correct for the amperage.

If the system was being used to produce 3 phase from a single phase primary feed- not a transformer but an MG (motor generator) set. THEN you would look at the sq rt of 3 on the output (secondary) side and obviously there would be no correction on the single phase "primary".

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#8

Re: Power Transformer Current Density

07/12/2012 8:00 AM

Your calculation gives the line current. The primary being delta connected, the current through the winding is 1/sq root 3.The vendor's calculation is correct.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Power Transformer Current Density

07/12/2012 8:31 AM

Amendment: My earlier answer was incorrect, as several others have noted. Thanks for catching.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bibo92004 (1); electronick (1); energygod (1); PeterT (2); Priyadarshan (1); sukumar75 (1); Tornado (2)