Dear friends,
In transformer Dyn11 when we give supply at D the LV supply will lead the HT By 30 degree,if we give supply at LV Side The HV side supply lead by 30 degree is it correct or not pl explain me
thank you,
Re: Transformer Vector Group
07/21/2012 6:06 PM
Try these: en.m.wikipedia.org/wiki/Vector_group www.control.com/thread/1026211688 (read the reply by Phil Corso. Im sure it will shed some light)
A wise man didn't become wise over night.
07/22/2012 8:24 AM
Good Answers: 170
07/29/2012 9:02 AM
Dyn11 means the HV winding is connected in Normal Delta and the LV winding is connected in Normal Star, with the LV neutral brought out. The LV voltage will lead the HV voltage by 30degrees.
Now, consider a 11kV/415V, Dyn11 Trf. Let us say, if, let us say, the (1U-1V) HV voltage is 11kV at an angle zero degrees, then the (2u-2v) LV voltage will be 415V at an angle PLUS 30 degrees. Conversely, if the LV voltage is 415V at an angle zero degrees, then the corresponding HV voltage will be 11kV at an angle MINUS 30 degrees.
But, make sure you don't apply even 415V (leave alone anything more) at the LV side and attempt to measure the HV voltage (11kV) directly. It might be catastrophic.