Dear all,

Do you guys agree if battery discharge test is carry out with frequency of every 2 years, it shorten the battery life. In my opinion, if the test is carried out without

reaching the minimum voltage limit of battery. it should be fine. I am talking about

industrial batteries bank (i.e 220VDC battery bank with 100-200 battery cells). Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Battery discharge test. Is it harmful to the battery life?

07/25/2012 12:13 AM

Look at it this way. The battery will last at least two years.

Register to Reply
Member

Join Date: Jul 2012
Posts: 7
#2
In reply to #1

Re: Battery discharge test. Is it harmful to the battery life?

07/25/2012 3:22 AM

industrial batter will last more than 10 years. I am still searching for literature explaning about effect of battery discharge test effect on battery life/

Register to Reply
2
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#3

Re: Battery discharge test. Is it harmful to the battery life?

07/25/2012 6:49 AM

You are obviously referring to a lead acid battery bank. Lead acid batteries do get in trouble if a cell battery goes under 2V. Now if you have a bank of 100 of 'em in series, there is no warranty that by keeping discharge voltage over 200V, none of the series cells will discharge to less than 2V, actually cell balance statistics say that MANY of them will. If you have the equipment to monitor ALL of them and stop discharging at the moment any of them is over-discharged (that's a joke), then yes there will be no harm done. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Good Answer (Score 2)
Member

Join Date: Jul 2012
Posts: 7
#4
In reply to #3

Re: Battery discharge test. Is it harmful to the battery life?

07/25/2012 6:58 AM

Yes. You are right Mr SimpleMind. I am working in power station. We have both lead acid and alkaline battery. As you point out, as long as we monitor the voltage, and the voltage maintain above the recommendation by OEM it should be fine right. Furthermore, the battery system function should be able to protect the protected system which is turbine etc. If a few battery cell fail, we just replace it. Not worth to save a battery which cost only a portion of the damage when it fail to work when needed. Thanks for your respond. I will relay this to my colleague. Awaiting other input and experience sharing. Thank you

Regards,

Shah

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #4

Re: Battery discharge test. Is it harmful to the battery life?

07/25/2012 10:36 AM

I believe, marine communication emergency power supply batteries were required to be tested this way.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/25/2012 11:54 AM

A critical point of doing a battery discharge test is to identify a failing battery before it is needed. Let's not forget this important aspect.

I agree that stopping the discharge before reaching the manufacturer's recommended minimum voltage should not significantly alter the lifetime of the battery.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Jul 2012
Posts: 7
#7
In reply to #6

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/25/2012 8:47 PM

my next question. How often do you carry out discharge test. Currently at my plant,

we carry out discharge test every 2 years. Is there any standard out there for this test? thank you.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#9
In reply to #7

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 12:02 AM

In merchant navy, battery capacity tests of emergency communication equipments are mandatory, every two years.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #6

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 4:38 AM

...and if it does, then the battery needs replacement, which is, after all, the point of the test.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#8

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/25/2012 11:17 PM

In a lead-acid battery plant like yours there are monhtly maintenance tasks to be performed: checking the torque on the terminals, measuring specific gravity in the individual cells to see how well they charge / discharge. As the cells are noticeable different capacity, you may have to charge them individually to even their status out.

Going every 3 or 6 months on battery supply only, gives a chance to measure voltage drop across contacts, with a chance to correct ones on the high side, after the test is complete.

After all of these a full load test can be performed. After all the preparations, It adds the information, how aged the cells are, to what degree they already lost their capacity to be charged. Without the former work and balancing the cells, the test is rather meaningless.

We are not talking about much time expended, maybe 3-4 hours monthly. Any repair is an add-on.

Lead-acid batteries last the longest in a fully charged floating condition. Full load test is needed be reasonably short, as the heat generated warps the plates and gradually loosens the oxide mass in the grid, by the heat generated.

Register to Reply
Power-User

Join Date: Jan 2010
Location: India
Posts: 166
Good Answers: 1
#10
In reply to #8

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 3:08 AM

If the battery is in float and near its full charge always, there is no need to discharge. There are portable equipment to measure impedance of each cells and you can be forewarned about health of each cell. You can see literature of Midtronics on this.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 3:43 AM

You have to tell us the type of battery as well for a proper answer......I could assume lead acid, sealed or not.....but would I be right?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#14
In reply to #11

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 9:12 AM

If we waited for a complete accurate survey of every ailing system before providing answers, this would be a very quiet forum.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 6:22 AM

If you don't test them you won't know what their condition is.

2 years is a pretty long interval.

There are battery monitoring systems that don't don't depend on discharging.

Guest1947 mentioned Midtronics. Cellwatch is another. Happy Googling.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2012
Posts: 31
Good Answers: 1
#15

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 12:23 PM

To discharge a flooded lead acid battery (biased on your description as industrial) to the minimum voltage limit is detrimental, and doing it at a rapid rate compounds the damage. I prefer to discharge to a standardized 50% depth of discharge, and examine each battery for voltage drop; logging the measurement so it can be compared to previous tests. Variations in specific gravity should be tested and logged to establish a trend in change. If a problem is found in one of the cell or a battery, then a discharge test can be preformed; it will probably end the life of the battery, and prove the need for replacement simultaneously. People in the business of selling batteries will not agree with this for obvious reasons.

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#16

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/26/2012 1:53 PM

I also worked in a power station and had responsibility to monitor our battery bank. Specifications required we had the ability to conduct emergency switching during a major power outage of 8 hours. We conducted monthly SG testing. A glance at the resultant records, with or without plotted graphs, quickly identified failing cells long before they failed the mandatory discharge test done once every two years.

As long as the cells are recharged right after being discharged, harm is minimal.

The discharge test should not be done before you have carried out normal maintenance such as SG test and topping up electrolyte. If you have the kind of cell casing equipped with bubbling tubes a cycle of bubbling to destratify the electrolyte is recommended. Monitoring all cells for temperature is also recommended. Incipient problems will often be revealed first as a rise in cell temp. Hand held IR meters are cheap enough there is no excuse for not using them.

__________________
Elnav
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#17

Re: Battery Discharge Test. Is it Harmful to the Battery Life?

07/27/2012 12:25 PM

Congratulations!

Every single contribution is a part to a teachable moment. Now, you know more, than most other people about maintaining batteries.

Best regards. And you owe us the results.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); elnav (1); Guest1947 (1); ijanto (3); Joshi (2); leveles (2); lyn (1); PWSlack (1); redfred (2); SimpleMind (1); Thomas J. Becker (1); Wal (1)

Previous in Forum: Geared AC Motors and Frequency Drives   Next in Forum: Select a Resistor

Advertisement