Generator Tripping on Rotor Grounding Protection Relay

07/27/2012 1:01 AM

our generator 325MW, 20kV tripped on actuation of rotor earth fault protection relay UNS 3020a-Z, Var. 1/2, make ABB

can any one tell me the reason

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: generator tripping on rortor grounding protectection relay

07/27/2012 3:08 AM

What was the outcome of the discussion with ABB's telephone technical helpline?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2012
Posts: 13
#2

Re: Generator Tripping on Rotor Grounding Protection Relay

07/28/2012 1:01 AM

It is quit clear that there is a earth fault on the rotor winding or earth fault relay problem. First try to trace one by one without being panic.

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#3

Re: Generator Tripping on Rotor Grounding Protection Relay

07/28/2012 9:19 AM

If the generator has tripped on actuation of rotor earth fault protection relay,the reason is supposed to be the occurence of rotor earth fault in the generator.Where is the doubt ?

In case you apprehend a mal-function,then you have to take up with the vendor/ABB for proper analysis of the matter based on the pre-trip & post -trip parameters available with you.

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Generator Tripping on Rotor Grounding Protection Relay

07/29/2012 8:10 AM

Are you suspecting spurious operation of the relay?

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#5

Re: Generator Tripping on Rotor Grounding Protection Relay

08/20/2012 1:21 AM

As already written by others, rotor earth fault is the reason. If you have doubt measure insulation resistance of rotor winding and get the same confirmed. If IR is OK in stand still condition, run the set after re-setting the relay and when circuit trips at certain speed, measure IR under that condition. If IR is still OK, contact relay supplier.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Milhan (1); pcchatur (1); PWSlack (1); spradhan (1)