our generator 325MW, 20kV tripped on actuation of rotor earth fault protection relay UNS 3020a-Z, Var. 1/2, make ABB
can any one tell me the reason
Re: generator tripping on rortor grounding protectection relay
07/27/2012 3:08 AM
What was the outcome of the discussion with ABB's telephone technical helpline?
Re: Generator Tripping on Rotor Grounding Protection Relay
07/28/2012 1:01 AM
It is quit clear that there is a earth fault on the rotor winding or earth fault relay problem. First try to trace one by one without being panic.
07/28/2012 9:19 AM
If the generator has tripped on actuation of rotor earth fault protection relay,the reason is supposed to be the occurence of rotor earth fault in the generator.Where is the doubt ?
In case you apprehend a mal-function,then you have to take up with the vendor/ABB for proper analysis of the matter based on the pre-trip & post -trip parameters available with you.
Learning is a never-ending process.
Good Answers: 170
07/29/2012 8:10 AM
Are you suspecting spurious operation of the relay?
08/20/2012 1:21 AM
As already written by others, rotor earth fault is the reason. If you have doubt measure insulation resistance of rotor winding and get the same confirmed. If IR is OK in stand still condition, run the set after re-setting the relay and when circuit trips at certain speed, measure IR under that condition. If IR is still OK, contact relay supplier.