How to connect 2-wire transmitter with 2 different PLC

07/28/2012 5:46 AM

A 2-wire pressure transmitter is now connected with Allen bradley Logix L63 series 1756-if8 module. I also require to take 4-20ma of this transmitter to another PLC of S7-200 Siemens make. Kindly guide m.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Active Contributor

Join Date: Jul 2012
Location: South Africa
Posts: 13
Good Answers: 3
#1

Re: How to connect 2-wire transmitter with 2 different PLC

07/28/2012 8:18 AM

If you configure the Siemens AI as a "passive" 4-20 mA input, you should be able to simply connect it in series...

If that is not an acceptable option you can also transfer the AI in the Allen Bradley straight to an AO that can again drive the AI on the Siemens (with or without loop isolator in between)

__________________
Living is more than mere existence and breath
Register to Reply Good Answer (Score 3)
Associate

Join Date: Sep 2011
Location: India
Posts: 28
#2
In reply to #1

Re: How to connect 2-wire transmitter with 2 different PLC

07/28/2012 2:30 PM

please tell what is passive input & how to configure? How to transfer the AI to AO?

__________________
I am man of simple taste.
Register to Reply
Active Contributor

Join Date: Jul 2012
Location: South Africa
Posts: 13
Good Answers: 3
#3
In reply to #2

Re: How to connect 2-wire transmitter with 2 different PLC

07/28/2012 3:28 PM

"Passive" input is when the loop is powered by an external source - not by the input card. "Active" input when the Analog input card supplies the loop (typical for 2-wire installations)

To transfer the AI to an AO, simply output the same tag (value that was read by the input) again to an output...

if you do have a "passive" input on the S7 (the S7 AI does not power the loop), you do not need the isolator. But in this case as mentioned earlier you can simply connect the two in series.

Note most Siemens S7 AI modules is configurable - you can change it from "active" (2-wire) to "passive" (3-wire).

__________________
Living is more than mere existence and breath
Register to Reply
Associate

Join Date: Sep 2011
Location: India
Posts: 28
#12
In reply to #3

Re: How to connect 2-wire transmitter with 2 different PLC

08/01/2012 4:51 AM

sir what i know passive output 4 to 20 mA is when transmitter is giving output by getting power from ai card hence generally all two wire are passive and active is when transmitter is giving output with its own power (may be some power source is available in the transmitter assembly ) . Typically 2 wire transmitter are passive.

__________________
I am man of simple taste.
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#9
In reply to #2

Re: How to connect 2-wire transmitter with 2 different PLC

07/30/2012 4:26 AM

Instead of bothering the world with a basic question you should have googled 4-20mA and read some of the technical stuff available.

This is basic knowledge.

Next question: how to configure the port of the Siemens PLC?

__________________
"Here we are now, entertain us"
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4
In reply to #1

Re: How to connect 2-wire transmitter with 2 different PLC

07/29/2012 8:22 AM

GA!

That will work as long as he stays within the common mode range of the input. This implies that both PLC are at the same ground level (same grid) and within a reasonable distance. There might be problems if other instruments are added in the loop.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Member

Join Date: Dec 2011
Posts: 7
#5

Re: How to connect 2-wire transmitter with 2 different PLC

07/29/2012 10:03 PM

You can use the 4-20 ma output by current multiplier and so on to numerous systems nothing problem***** kathirasan engineer electrical mtce

Register to Reply
Participant

Join Date: Jan 2011
Location: China, mars
Posts: 1
#6

Re: How to connect 2-wire transmitter with 2 different PLC

07/30/2012 12:20 AM

You can use a distributor for this.

one analog signal be into the ditributor and you can get two output signals for two dodules.

__________________
Rule is nature
Register to Reply
Participant

Join Date: Apr 2011
Posts: 4
#7

Re: How to connect 2-wire transmitter with 2 different PLC

07/30/2012 4:22 AM

hi

it is possible but not change the Aux voltage (power supply).in PLC analog i/p current is in series.

otherwise you put isolator

In transmitter (Rose mount) loop connection in our plant i connected series with Display monitor means.

power supply to transmitter series with PLC and Display monitor system.

if it series connection it possible.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: How to connect 2-wire transmitter with 2 different PLC

07/30/2012 4:24 AM

If none of the above is practicable, re-transmit the signal going into one PLC to the other using a re-transmit unit. Lee Dickens (usual disclaimer) does a range of solutions for instrumentation hook-up problems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10

Re: How to connect 2-wire transmitter with 2 different PLC

07/30/2012 9:55 AM

JPV has hit it right. However if you don't have the AO card and don't want that expense, Precision Digital has several panel meters that have an optional 4-20ma re-transmitter that is definitely cheaper than most AO cards. You can hide the panel meter display or use it as a local display. Be aware that 4-20ma to digital display conversions are best kept to a minimum because you will not get exactly the same reading (referring to the 0.01 place) on multiple displays over entire process ranges.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Active Contributor

Join Date: Jun 2007
Posts: 18
Good Answers: 1
#11

Re: How to connect 2-wire transmitter with 2 different PLC

07/30/2012 5:24 PM

Add a current-to-current isolator to the transmitter output and connect the two isolator outputs to the PLC inputs. Each current output is loop powered from the 2 PLCs.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Gwen.Stouthuysen (1); jeetu (2); JPV (2); marcot (1); Pete (Contol Systems) (1); Phys (1); PWSlack (1); qugd (1); rishikathirasan (1); sunildatta (1)

Previous in Forum: Silica sand to fill the space on thermowell   Next in Forum: Intools Training Course

Advertisement