Voltage Drop

07/30/2012 1:07 AM

Dear Gurus,

I have one problem with my existing supply.

My transfomer is 630 KVA, 22000/433 volt, 50 Hz operating at 0.92 P.F.

It is feeding two different areas , first by 1* 3.5 c *300 sq. mm Al. Arm. cable which is 50 meters in length ( load is 150 KVA ) and second is 560 meters length with 2* 3.5 c * 300 sq. mm cable ( load is 300 KVA), I have calculated drop which comes around 10 volt in second case.

Now my query is can I install a capacitor bank for second feeder to boost voltage at load end as i am getting 200 volt only , and other reason is that I can not increase transforner tapp which would cause higher voltage in first feeder.

Please give your opinion.

regards,

santosh.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: VOLTAGE DROP

07/30/2012 3:59 AM

What is the specified tolerance on the voltage of the LV side of the transformer at the customer's incoming terminals, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jul 2012
Posts: 5
Good Answers: 1
#2

Re: Voltage Drop

07/30/2012 2:46 PM

Is the voltage at the transformer 433 volts? Is the 200 volts you mentioned phase to neutral? What should it be? What is the phase to phase voltage at the end of the cable?

Register to Reply
Member

Join Date: Jan 2011
Posts: 7
#3

Re: Voltage Drop

07/30/2012 11:15 PM

1. What is rating of ur installed Transformer (KVA)?

2. What is the Phase to phase voltage on LV side of thranformer ends on running load of Area -1 & Area- 2. ?

3.What is the the phase top phase voltage on second ends of the cables (Load Area End) ?

4. What is the running load & PF of cables Area-2 ?

5. What is the ambient and cable temperature on operation time ?

__________________
dark shadow
Register to Reply
Associate

Join Date: Nov 2011
Location: mumbai
Posts: 28
#5
In reply to #3

Re: Voltage Drop

07/31/2012 12:40 AM

Sir,

The transformer is 630 kva, voltage near transformer is 415 volt phase to phase and 350 volt , phase to phase near second feeder end.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Voltage Drop

07/31/2012 3:40 AM

Measure the voltage drops across any terminations. Something is resistive.

Do you have an IR camera?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #5

Re: Voltage Drop

07/31/2012 8:50 AM

Is it the same on every phase?

Is the phase loading balanced (same current on each)?

Have you checked the batteries in your Infrared camera yet?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Voltage Drop

07/31/2012 12:22 AM

Capacitor bank is for PF correction.

What sort of loads do you have?

You are a bit stingy with collected data mate. You need to share it (if you actually have it) in order for anyone to make a proper recommendation.

Aluminium conductors, hmmm....., who supervised the termination of these?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#7

Re: Voltage Drop

07/31/2012 5:38 AM

Dear Mr. Santosh

We will calculate the voltage drop in volt as well as voltage drop in % which is more meaning full. We need some confirmations & some more clarification which are as follows:

A. Conformation

1. Transformer is rated KVA is 630

2. Transformer Primary Voltage is 22000V or 22KV & 3-Phase

3. Secondary Voltage is rated 433V & 3-Phase

4. There is no meaning for 0.92P.F. for transformer

5. Second cable which is 2* 3.5 c * 300 sq. mm cable, is Al. OR Cu

B. Clarifications

1. Read on transformer name plate what is the % Z or percent impedance

2. Tell us each load serving P.F. otherwise we will take general value as 0.85P.F.

3. Your mentioned Voltage 200 is Phase to neutral

4. All cables are rated to 433V or 600V

5. Unless you know the Power factor of the second load do not try to think of connecting the capacitor bank. Capacitor bank for P.F. Improvement but not for Voltage drop improvement

6. Your calculated voltage drop of 10V is Phase to Phase or Phase to Neutral

__________________
B.E, M.I.E, M.S
Register to Reply
Associate

Join Date: Nov 2011
Location: mumbai
Posts: 28
#8
In reply to #7

Re: Voltage Drop

07/31/2012 5:59 AM

Dear Sir,

Transformer is 630 KVA , 22KV/.433 KV, delta / star connected.

second cable is aluminium, 1100 volt rated.

I have taken p.f on transformer side. we dont have pf meter on load side in second case so can not measure.

0.92 pf is showing in MSEDCL meter.

200 is phase to neutral voltage.

Regards,

santosh.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #8

Re: Voltage Drop

07/31/2012 9:03 AM

At 415V p-p, you will expect ~240V P-N

if 10% drop is accepted, then you should aim at 216V P-N

If at the transformer you are getting 415V P-P, you should aim at 216V P-N at the end of the 560m.

Having 200V means that your drop is about 15% (High!).

For a 300kVA load, the maximum current will be ~ 418A at P.F.=1

If your P.F. is 0.8, to get a 300kVA loading will draw 522A

If your P.F. is 0.7, to draw 300 kVA loading will draw 597A

Therefore, Depending on the load and P.F. of the load, you can easily exceed the current drawn on these cables.

What is missing from your info:

Check the No-Load voltage at the end, then the normal load voltage you are getting, by measurement.

Also, measure the current at that load.

these will give you your real voltage drop and you can estimate the % drop.

If the Load is supplied through a Watt meter and a VAR meter (kWatt and KVAR or even KVA), these will help you calculate the P.F. without a meter. All digital power meters have the facility to give you the P.F.

there are many cable size callculators available on the net (or Cable sizing tables with Voltage drop rates...) to help working out the size required, provided you get the required values to input.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#11

Re: Voltage Drop

08/01/2012 8:18 AM

Normally, Capacitor bank is not used for voltage boosting purpose; it is being used for improvement of Power Factor.As for solution of your problem, please check the cable terminations to detec loose connections,bad crimping of cable lugs etc. which may increase the contact resistance, the effect of which may be voltage drop along with abnormal heating of terminations and subsequent failures.Also please check the voltage regulation of the above transformer.You have not mentioned the type of load;many things depends on the type of load; for example,if the harmonics content are high (THD & THVD), additional currents may flow due to the harmonics.

Thanks,,

Manindra.

__________________
Manindra
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12

Re: Voltage Drop

08/01/2012 12:30 PM

That voltage drop is doing work somewhere.

Do you have a non-contact thermometer?

Read.

Digest.

Get on with it!

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#13

Re: Voltage Drop

08/03/2012 8:09 PM

The voltage drop in 2 parallel cables is 6.67% at P.F= 0.8, and corresponding voltage at load end is 404.1/233.3V.

If 3 cables are connected in parallel, then voltage drop will improve from 6.67% to 4.45% OR 404.1/233.3 to 413.7/238.8V

It is also required to chech the voltage at transformer teminal when both the full loads are connected.

If the Translformer with Z% of 7.5 or 7.5 per unit, at 650Amps, it shall not be dropped in transformer more than 18.75Volts phase to neutral.

__________________
B.E, M.I.E, M.S