Cable Laying Procedure

07/31/2012 7:36 AM

Dear sir,

I have 7 nos of temperature sensors in different locations. I used 1Px1.5sqmm cable for connecting sensor to the PLC. Actually the PLC panel location is far away, approx 200m. So a junction box is installed and all the 7 sensor cable are terminated in the junction box.

Now, the question is from the juntion box to PLC, whether I have to lay 7 Nos of 1Px1.5 sqmm cable or Can I use 10P or 12P x 1.5 sqmm cable?

Can I use multipair cable to club the analog signal from the sensors?

What are the practical difficulties, if I use 12P cable for reduce the number of cables? Is any other possible way or any standard procedure, please kindly clarify.

Regards,

Kailash

Register to Reply
Pathfinder Tags: cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable Laying Procedure

07/31/2012 7:39 AM

The above description reflects the use of multipair cables elsewhere. Go for it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Cable Laying Procedure

07/31/2012 8:39 AM

If one were to run 7 individual cables back to the PLC, then one wouldn't need the junction box.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Cable Laying Procedure

08/01/2012 3:28 AM

That depends on the availability of it at your location.

Are you really using 1Px1.5mm2 or is it really 2x1.5mm2?

__________________
Difficulty is not an obstacle it is merely an attribute.