Cable Sizing for 100% UL MCCB's for Diesel Generator Application

08/08/2012 5:17 AM

Hi Folks,

I'm working on a project at the minute and wanted to gather some information that may help me or find out if someone has come across the same issue. Please see the following:

I am sizing cabling for a diesel generator application. The market requirements are for 100% UL rated circuit breakers specfically an ABB circuit breaker 800A and less. I've been reviewing the standards and UL states that the breaker terminal temperature must not exceed 75ºC using 90ºC cable. This is pretty straight forward however cable sizing for UL requires us to look at NFPA70 (NEC2011). This is where it is confusing me. In the application we are using a trunking or conduit if you will between the circuit breaker enclosure and the alternator which is not untypical of this type of machine. The problem is when looking at the correction factor tables and the various tables for sizing cable according to NEC 2011 (article 310) they seem to be primarily for customer wiring to the breakers and not factory wiring. Also on top of this the tables state values either for in free air or in a raceway, cable or directly burried which in my eyes is a big jump from our application. In a cable, raceway or burried would lead me to believe that there is no air flow where as in my application although there might not be a lot of moving air there is some. This is the dilema I face as im trying to calculate without testing thus far but i'm starting to convince myself that testing is the best way.

Any information would be greatly appreciated. Thanks.

Would just like to know if anyone has come across anything similar.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Cable Sizing for 100% UL MCCBs for Diesel Generator Application

08/08/2012 2:40 PM

If you are building something in the field, you use the NEC. If you are building something as an OEM, you would use whatever listing authority specification for your equipment is applicable, and that usually ends up being UL if you are in North America. So if you are using the 100% rated breaker in "switchgear", then the UL file for the type of switchgear is what counts, if you are using it in a "control panel", then UL-508 is what counts, and if you are using a single breaker in its own enclosure with nothing else, i.e. an "enclosed circuit breaker", then UL-489 is what counts. I mention this because enclosure sizing is critical to be able to use 100% rated breakers, so you either have to use enclosures that are already listed to house a 100% rated breaker, or you must label the system in such a way as to designate a specific air volume that must be maintained to be able to use them. Most people are unaware of that little twist.

In those standards there are rules for conductor sises that do not necessarily follow the NEC, but for the most part they do. So bottom line if you use the NEC rules, you will be covered, but you MIGHT be able to get away with something less if you are listing it under a UL standard.

So if you are going to use the NEC, it's spelled out for you in Article 215.2(A) and the exceptions that apply to that. 90°C rated conductors, but sized per the 75°C charts.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#3
In reply to #1

Re: Cable Sizing for 100% UL MCCBs for Diesel Generator Application

08/08/2012 11:26 PM

And this is why this site is one of the most important sites that exists today.

Not only to follow NEC, NFPA, but also UL. And when to follow which!

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4
In reply to #1

Re: Cable Sizing for 100% UL MCCBs for Diesel Generator Application

08/09/2012 3:33 PM

Sir,

JRaef has it right. I will add that the enclosure size rules also are to allow adequate space for the bending radius of the conductors.

The reason for the 75°C column limit for 90°C rated cable is because the breakers are tested and rated for proper operation with their terminals not getting any hotter than the 75°C limit in an ambient temperature not exceeding 40°C. If your breaker is in a higher ambient location, then additional derating of the cable size will be needed. Cables with 90°C insulation are often desirable for use because they allow a higher current or allow for temperature or conduit fill derating. However, in your case, you have to use the 75°C table because of the limit on temperature at the termination.

--JMM

Register to Reply
Associate

Join Date: Jan 2008
Posts: 43
#5
In reply to #1

Re: Cable Sizing for 100% UL MCCBs for Diesel Generator Application

08/23/2012 5:50 AM

Thank you for you reply. The information you provided is generally what I have been finding there is actually an additional requirement that may change between breaker manufacturers and that is they list them with specific cable lug terminals also and therefore we must use them to avoid re-cert.

With these 100% rated CB's we are required to follow ABB's listing instructions (cable sizing to 75ºC, specfic box sizes, bend radii of cabling and terminal lugs) according to ABB's UL listing to UL489. If we deviate we must have a review with UL and that is pretty clear. What I am trying to gather is a level of confidence before testing (as this is probably going to have to happen anyway). I am trying to gauge what table would be most applicable to my application and i've found some information that I would like to get someone else's opinion on.

I have the NEC2011 with me and i've noted somethin that i've found. There is an information note:

"Adjustment factors shall not apply to conductors in raceways having a length not exceeding 600mm (24in.)."

The raceway i am installing the cables through (from the alt to the breaker) is less than 600mm. This would say to me that bunching factors are no longer required the same as ambient de-rates are no longer required.

The question I am facing at the moment is are the bunching factors and the de-rates as per tables 16 & 17 still applicable considering the raceway is less than 600mm? In which case I could use current values for cabling the breaker based on single conductors in free air table 310.15(B)(17) instead of using table 310.15(B)(16).

Your thoughts?

Best regards.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#6
In reply to #5

Re: Cable Sizing for 100% UL MCCBs for Diesel Generator Application

08/25/2012 12:23 AM

Sir,

Regarding de-rating, I believe the only one you can ignore is the conduit/raceway fill. All these code considerations for wires and cables are based on the need to keep the conductor insulation temperature within safe limits. Free air has easy radiation and convection. When the ambient temperature is higher, the radiation and convection are reduced, so ampacity is correspondingly reduced (depending on the difference between the ambient temperature and the conductor's insulation temperature limits). When more conductors are in a given conduit/raceway, then you must assume that each one is carrying the current it is rated for and you have more heat sources trying to be cooled by radiation or convection from the outside surface of the conduit. However, when the conduit/raceway is fairly short then conduction of excess heat along the length of the conductors will also help to reduce their temperature. For this reason, the code permits the conductor fill (only) to be ignored when calculating ampacity.

If you are purchasing components and assembling them together without additional testing and listing of your finished product, then you must comply with all the requirements of the listing for each component. This includes the maximum temperature rating for the conductors attached to the breaker terminals (you can use a conductor with a higher-rated insulation temperature, but must limit its ampacity to either the 75 or 90 degC table (depending on the breaker's rating).

If you are having your completed product assembled and tested to the U/L standards, then you would go by their book and can frequently use a smaller conductor size. In the mid- to late-90's I worked in a U/L panel shop and met with their inspector a couple times when he was by to see what we were doing (all custom jobs) and verify that we were complying with their rules.

Hope this helps.--JMM

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Cable Sizing for 100% UL MCCB's for Diesel Generator Application

08/08/2012 4:02 PM

Jraef is exactly correct.

If you are not having your work inspected by a UL Inspector, you MUST follow NEC.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

gowdy87 (1); Jimh77 (1); jmueller (2); JRaef (1); WJMFIRE (1)

Previous in Forum: Regarding Rotation of Ceiling Fan and Table Fan(Single Phase Induction Motor)   Next in Forum: Frequency Change in the Grid

Advertisement