Hi Folks,
I'm working on a project at the minute and wanted to gather some information that may help me or find out if someone has come across the same issue. Please see the following:
I am sizing cabling for a diesel generator application. The market requirements are for 100% UL rated circuit breakers specfically an ABB circuit breaker 800A and less. I've been reviewing the standards and UL states that the breaker terminal temperature must not exceed 75ºC using 90ºC cable. This is pretty straight forward however cable sizing for UL requires us to look at NFPA70 (NEC2011). This is where it is confusing me. In the application we are using a trunking or conduit if you will between the circuit breaker enclosure and the alternator which is not untypical of this type of machine. The problem is when looking at the correction factor tables and the various tables for sizing cable according to NEC 2011 (article 310) they seem to be primarily for customer wiring to the breakers and not factory wiring. Also on top of this the tables state values either for in free air or in a raceway, cable or directly burried which in my eyes is a big jump from our application. In a cable, raceway or burried would lead me to believe that there is no air flow where as in my application although there might not be a lot of moving air there is some. This is the dilema I face as im trying to calculate without testing thus far but i'm starting to convince myself that testing is the best way.
Any information would be greatly appreciated. Thanks.
Would just like to know if anyone has come across anything similar.