how to measure the earth resistance on a panel board? what is the limited value?
Engineering Fields - Power Engineering - Projects Engineer
Re: earthing and neutral
08/11/2012 3:11 AM
i think you need to measure the EARTH LOOP IMPEDENCE.
this is best done by a good ELI tester.
this test is on live circuit and you will need to utilise a service of a qualified person.
as regards to the values.this will depend on the protection used..fuses,Mcb class etc.
generally between 0.8 to 3 ohms?
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
08/11/2012 3:16 AM
i have tried to measure it with the common mutlimeter. i have not got a fixed resistance value " that was varying" . i hava tried to measure the voltage between earth and neutral. that was a bout 1.35 v.
is that value can b considered good?
08/13/2012 3:31 AM
Yet again for this forum, a voltage between earth and neutral is simply a feature of the neutral current and the earth loop impedance. It is neither good nor bad; it just is.
Consult a qualified electrician.
  • What's black and hangs from the ceiling? An electrician that doesn't know what he is doing....
Re: Earthing and Neutral
08/13/2012 3:33 AM
The qualified electrician that installed the board will measure it using test equipment and issue the occupier with a test certificate that says what it is.