I.S. Solenoid Valve

08/12/2012 3:37 AM

Hi,

I am using I.S. solenoid valve(24vDC) with MTL barrier. Cable used for solenoid is 0.75mm(sq.), distance between barrier and solenoid valve is 35 mtrs. I have done cable sizing and found out that size is ok and voltage drop is less than 1.5%. My question is

1. How to ensure that cable can carry sufficient current supplied by barrier required for solenoid operation? Is there any calculation ?

2. Which solenoid valve current shall be used , Inrush or holding current ?

Pl. let me know if I am thinking in right direction considering current requirements.

thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Dec 2011
Posts: 4
Good Answers: 1
#1

Re: I.S. Solenoid Valve

08/13/2012 12:26 AM

You should mentioned Watt (coil power useage).

Both the inrush current and Holding current are important.

Register to Reply
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#2

Re: I.S. Solenoid Valve

08/13/2012 12:29 AM

INRUSH current is mandatory

__________________
devitg
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #2

Re: I.S. Solenoid Valve

08/13/2012 9:16 AM

Is there an inrush current in a DC solenoid ? Not unless there is an economy-resistor/double coil solenoid. Even then, the inrush is momentary, and must be integrated knowing the duty cycle...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: I.S. Solenoid Valve

08/13/2012 1:48 AM

1. How to ensure that cable can carry sufficient current supplied by barrier required for solenoid operation? Is there any calculation ?

The same way that you worked out that the voltage drop was acceptable.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: I.S. Solenoid Valve

08/13/2012 3:52 AM

A1a) Test it.

A1b) Compare it with installations elsewhere.

Bear in mind that it is not the solenoid valve that is intrinsically safe. It is the method of protection of the hazardous area that is instrinsically safe provided all the components including the solenoid valve are designed, selected and installed so as to form an intrinsically safe system.

  • At 35m, another option would be to put the solenoid valve in a safe area and run an air line to the equipment in the hazardous area. That way, the barrier can be dispensed with.
  • Another option, provided the solenoid valve was in either Zone 1 or Zone 2, would be to use a solenoid valve that was EEx d - "flameproof" - and dispense with the barrier.

Do not design, specify, install or maintain hazardous area electrical equipment without having undergone a suitable training programme.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#5

Re: I.S. Solenoid Valve

08/13/2012 4:01 AM

In an intrinsically safe circuit the voltage drop is less important than the amount of energy stored in the cable. View the cable as a capacitor/inductor in series with your solenoid. The barrier limits the amount of energy passing into the hazardous area to a level so that if a fault were to occur, the resulting spark would not be sufficient to ignite the gas. Too much energy stored within the cable renders the barrier useless. Do not rely on any advice provided by this sort of forum. Make sure that you take expert advice. Your MTL rep will be trained to help you, and will have recommendations and tables available.

Register to Reply
Active Contributor

Join Date: Feb 2012
Posts: 11
Good Answers: 1
#7

Re: I.S. Solenoid Valve

08/13/2012 9:19 AM

Hi

thanks all for your valuable advice.

thanks.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: I.S. Solenoid Valve

08/13/2012 10:30 AM

Go and get that training.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Control Engineering - Newby Member Long Time User Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jun 2006
Posts: 224
Good Answers: 9
#9

Re: I.S. Solenoid Valve

08/13/2012 10:59 AM

if the valve is truly rated for a hazardous environment, then the manufacturer is required to supply a "Control Drawing" which shows how the device is to be used. Refer to the manufacturers specifications first, then proceed with your other calculations.