Minimum Cross Section Required for Short Circuit

08/14/2012 1:59 AM

IEC 61439 specfies minimum cross section required for SC currents as CS= sqrt(I(square)*t)/k .. ..here I is the current t is the short time current (from 0.1 to 5s maximum) and k value depends on factors like material, temperature , type of sleeving etc. Now IEC considers max. temperature rise of conductor during short circuit to be 250 degree celcius...should 250 degree celcius be considered as a limitation imposed by standards or can the maximum temperature be stretched to more than that since Melting point of materials like Cu or Al is much higher...is this limit specified keeping in mind the melting point of insulating supports that shall be in contact with the conductors during a short circuit..?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Minimum Cross section required for Short circuit

08/14/2012 3:13 AM

<...should 250 degree celcius be considered as a limitation imposed by standards or can the maximum temperature be stretched to more than that since Melting point of materials like Cu or Al ...>

Wouldn't that turn the conductor into a fuse?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#2
In reply to #1

Re: Minimum Cross section required for Short circuit

08/14/2012 5:22 AM

I am not saying the max limit should be equal to the melting point of the condcutor..but even if it is half the maximum temperature could be around 500 degrees in case of copper..

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Minimum Cross section required for Short circuit

08/14/2012 5:59 AM

OK. What is the melting point and the auto-ignition point of the insulation that encloses it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Minimum Cross Section Required for Short Circuit

08/14/2012 10:48 AM

What's your operating temperature?

Let's say ambient temperature is 50°C. Conductor temperature is 60°C. Now add

250°C.

That puts you at 310°C. You want to stretch that???

Common insulation will have run off the wires long ago.

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#5
In reply to #4

Re: Minimum Cross Section Required for Short Circuit

08/14/2012 12:06 PM

Intelligence either is, or it ain't.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Minimum Cross Section Required for Short Circuit

08/14/2012 11:26 PM

Thank you for proving the point.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Minimum Cross Section Required for Short Circuit

08/14/2012 10:43 PM

Cable manufacturer's catalog gives SC current withstand for each size of cable

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Minimum Cross Section Required for Short Circuit

08/21/2012 9:05 PM

First of all your formula is wrong. It should be:

S = I Root (t) / K

S = Cross section of the conductor, in sq.mm

I = Fault current in Amperes

t = Fault duration in seconds

K = Adiabatic Constant

(In your formula, the 'k' in the denominator should have been squared and then the whold square root taken for it.)

Now, as regards the temperature limits, (250 degrees C) it is to limit the damage to the insulation (like PVC) of any cable conductors that shall be in contact with the conductors. PVC tends to soften at about 200 Degrees C.

If you make a careful study, for bare conductors, the adiabatic constant 'k' is taken considering a much higher temperature (of the order of 600 Degrees C).

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); kushal_1206 (1); lyn (2); pnaban (1); PWSlack (2)