Can anybody tell the formula to calculate the fault current flowing in neutral line?
Pathfinder Tags: Neural fault current
Re: Electrical Engineer
08/14/2012 3:12 AM
As fault currents usually flow in the earth conductor until such time as the circuit protective device operates, it will prove to be extraordinarily difficult.
08/14/2012 6:23 AM
Ahah! A formula! OK:
  • Consider a phase-to-neutral fault in a single-phase system, with Ip flowing in the phase conductor. If In is the neutral current, then In = Ip, again only until the circuit protective device operates, at which point In=Ip=0.
Will that do?
Good Answers: 445
Re: Calculate the Fault Current
08/14/2012 10:27 AM
There is no single formula since the fault current depends upon the overall system configuration (isolated, networked), what types of loads (resistive, inductive, capacitive) are in the network, the exact nature of the fault (single line to ground, three phase to ground, etc.), and the length of time the fault exists (intitiation, 5 cycles, 1 second, etc.). For simple configurations you can use symmetrical components, otherwise the best "formula" is to use a commercial software package such as ETAP.
A quick look at section 8 in this paper will give you an introduction to some of the formulas (symmetrical components) and methods (per unit system) used by power engineers to analyze the more common faults, but note that this only considers the steady state values, not the dynamic time varying values during fault initiation and decay, that's a whole other topic unto itself. Google is your friend and teacher.
02/21/2024 10:06 AM
There is content in British Standard 7671 on this topic. Any qualified electrician can handle the formula and carry out the calculation.