DO WE NEED 25 SYN. CHECK RELAY IF SAME TRANSFORMER APPLIED???
Re: DO WE NEED 25 SYN. CHECK RELAY IF SAME TRANSFORMER APPLIED
08/20/2012 11:20 PM
LET ME CHECK.
08/21/2012 1:32 AM
What did you come back with Lyn? After all the shouting its ringing in my ears.
Maybe one Syn. Check relay is sufficient?
08/21/2012 3:30 AM
IT'S DIFFICULT TO SAY AS THE CONTEXT IS MISSING.
Good Answers: 59
08/21/2012 7:01 AM
Please avoid writing your post in all CAPS. On the Internet this is considered shouting at the people who read your post. Nobody likes to be yelled at.
08/21/2012 4:37 PM
Are you referring to a 25 Sync relay?
08/21/2012 10:11 PM
yes.is a syn check relay.
basically the 2 tx input to the switchboard are same model,same type.
if same model & same type,it should have same vector,angle.
hence,do we still need to run syn check before we close the breaker??
08/23/2012 8:29 AM
If the 2 transformers are fed from 2 different sources of supply ( viz:utility supply /captive power plant source ) check sync relay is a must even if the 2 transformers are identical in all respects.
If both the transformers are fed from the same source,the said relay need not be considered.However,some clients go for the relay in all the substations for standardisation/uniformity purpose.
Learning is a never-ending process.
Register to Reply 7 comments
IdeaSmith (1); lyn (1); PWSlack (1); SavvyExacta (1); spradhan (1); wareagle (1); zagu12 (1)