Centrifugal Chiller

08/23/2012 10:44 AM

I have about 25 year old trane centrifugal chiller. It has a new water tower and condencer tubes have been cleaned and keeps a condencer temp at 84. the chiller is now running at full amps and can not keep the water under 50 digrees. it has a 6.75 approach. It is also fully loaded as it is doing this. Any suggestions?

Register to Reply
Pathfinder Tags: centrifugal chiller
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: centrifugal chiller

08/23/2012 10:57 AM
  • Maybe it has had additional equipment added to the circuit in the last 25 years and is undersized.
  • Maybe the outside air humidity is so high that the cooling tower is currently undersized.

How well does it work in the winter?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Aug 2012
Posts: 2
#2
In reply to #1

Re: centrifugal chiller

08/23/2012 11:08 AM

Good in winter. Its the towers first summer but there is another chiller and it works fine. Keeps 44 digrees. I'm thinking low on refrigarent. Or on its last leg. Any tips or tricks to keep it alive?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3
In reply to #2

Re: centrifugal chiller

08/23/2012 11:44 AM

You didn't give units for temp., I think it is deg F. Just compare its all parameters like compressor suction and discharge pressures and temperatures, water flow rate to evaporator and condenser with the chiller running fine. you may yourself get the answer. Or else, give those figures here.

Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: Centrifugal Chiller

08/23/2012 2:50 PM

So you have a chiller with a water-cooled condenser chilling a water loop, correct? Is the 84degF the water temp leaving the tower or the actual refrigerant condensing temp?

The following info would be useful: Tower water temp entering condenser, tower water temp leaving condenser, tower water flow rate, chilled water temp entering evaporator, chilled water temp leaving evaporator, chilled water flow rate, condenser refrigerant presure, evaporator refrigerant pressure, chiller rated capacity and conditions, refrigerant used

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Centrifugal Chiller

08/24/2012 12:09 AM

Also, what is the wet bulb temperature? (Or location.)

From your symptoms, an overcharge of refrigerant seems more likely than an undercharge.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Centrifugal Chiller

08/24/2012 3:27 AM

What sort of advice came from the chiller manufacturer in response to the telephone call to their technical helpline?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856