Line Differential

08/27/2012 7:04 AM

We have "10Km Line" in a 63/20KV Substation.

for this Line, Which Protection can we Consider?

Line differential or Distance?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: line differential

08/27/2012 7:43 AM

It's a big substation with a 119Km line in it!

Don't post duplicate threads!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Line Differential

08/27/2012 2:50 PM

You can consider both types of line protection relaying, but a qualified protection engineer could tell you which is preferable. There are likely other pieces of information that will be required, such as is there generation at one end or the other (or along the line), is there a requirement for fast tripping (5 cycles or less), any requirements from your electric utility, or other considerations.

Remember too that differential protection will require some sort of communication path along the 10km path of the line, so that the differential relays at the ends can communicate with each other. Differential won't work if the relays can't compare what goes in to what comes out. Distance relays work just from their end by looking at line impedance.

Hire a qualified professional to determine this for you.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#3
In reply to #2

Re: Line Differential

08/27/2012 11:51 PM

Thank you for your Reply.

But I have a Question?

Which Parameter can we Clear to select Line Differential or Distance Protection.

I am Designing of Protection System for 63/20KV Conventional Substation.We have 2*63KV Incoming Line Feeder,2*63KV Outgoing Line Feeder,1*63KV Coupler(With Disconnector Switch),2*63/20KV TR. Feeder,12*20KV Outgoing with 1*20KV Coupler.

LINE DATA:

RL : 0.1771 Ω/Km , XL : 0.394 Ω/Km , L : 13.5km

Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #3

Re: Line Differential

08/28/2012 7:47 AM

And I'm telling you that you could use either, depending on the situation.

If you want the fastest, most sensitive protection, the line differential will be your better choice. However, you will need to put relays at both ends of the line (so you need access to the station at the other end, or the cooperation of its owner), and have a communication path between them for the differential scheme to work.

If there are no requirements for extremely fast, sensitive protection, use line distance relays. They are the simplest and least costly. They are used for probably 90% of line protection schemes.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#5

Re: Line Differential

09/12/2012 8:48 AM

You can use either. You didn't even specify if the lines is radial or not, which in my point could even point to using overcurrent current relays.. hahaha..

But always consider the fault resistance reach in settings if using such relays.

Register to Reply