Earthing & Grounding
08/27/2012 12:59 PM
what is difference between earthing & grounding ?
Re: Earthing & Grounding
08/27/2012 1:03 PM
Semantics. No difference practically.
Good Answers: 46
08/27/2012 2:02 PM
Have a look here for the basics on Earthing and Grounding. There a little more to it than Semantics.
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Good Answers: 140
08/27/2012 2:33 PM
Essentially... the Atlantic Ocean. In North Ameirca we call a conductive connection to the mass of the earth "ground" and the process of making that connection is called "grounding". While in Europe (and many other places) that connection is called "earth" and the process of making that connection is called "earthing".
No matter how you say it... it is the practice of connecting an electrical circuit (and there are numerous ways of doing so) to the mass of the planet.
Good Answers: 44
08/27/2012 3:42 PM
What is the difference between POSTING and SEARCHING on CR4?
08/27/2012 7:54 PM
Not all posters are SEARCHING; not all searchers are POSTING.
Not all grounds go to earth. There is no ground in space.
08/27/2012 7:43 PM
There is confusion when you use the term earth. Are you referring to earth(dirt) or are your referring the the neutral of the system. An earth(dirt) fault has a high resistance and current flow is a low value. A Phase to neutral(sometimes called ground) fault will have a low impedance and the current flow is a high value. Regarding distance, the fault will flow back to the source. Earth(dirt) is not a "sink hole" and does not absorb the fault current.
Earthing , seems to mean a connection to mother earth(dirt). Earthing a piece of equipment will not provide safety in the event of a fault. The resistance of the earth is too high to allow enough current flow to trip a breaker. Bonding or grounding the equipment is the method used in the US to cause the breaker to trip. An Equipment Grounding Conductor EGC is installed with the power conductor and connected to the equipment. The EGC is bonded to the metal frame at one end and to the Main Switch and grounding electrode at the other end. This provides a path for the fault current to flow.
08/28/2012 3:41 AM
The Atlantic Ocean.
Good Answers: 170
08/29/2012 9:47 AM
Myth: 'Grounding' implies connection of current carrying parts to ground, like transformer or generator neutral and 'Earthing' implies connection of non-current carrying parts to ground, like metallic enclosures.
Fact: As per IS 3043-1987, vide Cl. 0.7, the terms 'earthing' and 'grounding' are synonymous. Perhaps the different nomenclature is due to the usual conflicting usage of English language between the Americans & the British. While the British termed it as 'earthing', the Americans termed it as 'grounding'. IEC & IS Standards refer as 'earthing', while IEEE & ANSI Standards refer as 'grounding'.
To quote from IEC 60050: "The terms 'earth' as well as 'ground' have both been in general use to describe the common power/signal reference point interchangeably around the world in the Electro-technical terminology. While the USA and other North American countries favor the use of the term 'ground', European countries including the UK and many other Eastern countries prefer the term 'earth'".
To quote from "Earthing Practice" - CDA Publication 119 - 1997 (vide BS 7430:1991 Code of Practice for Earthing): "It is worth noting that in Europe we tend to use the term earthing, whilst in North America, the term "grounding" is more common.
The IEEE definition of grounding is: "Ground (ground system) - A conducting connection, whether intentional or accidental, by which an electric circuit or equipment is connected to the earth or some conducting body of relatively large extent that serves in place of the earth."
For use within Europe, if the generally accepted terms were replaced as below, then the meaning remains the same.
"Earth (earth system) - A conducting connection, whether intentional or accidental, by which an electric circuit or equipment is connected to the mass of earth or some conducting body of relatively large extent that serves in place of the mass of earth."
Register to Reply 8 comments