DP Level Transmitter

08/27/2012 12:56 PM

Can anyone explain to me what is the difference between DP level transmitters that Low side tapping connected at the top and High side tapping at the bottom. while some HIGH side tapping connected at top, LOW side tap at bottom.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#1

Re: DP Level Transmitter

08/27/2012 2:12 PM

Here some basics. Hope it helps.

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: DP Level Transmitter

08/27/2012 2:19 PM

Not very clear:

"that Low side tapping connected at the top and High side tapping at the bottom. while some HIGH side tapping connected at top, LOW side tap at bottom."

Perhaps you could post a sketch or more detail....

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: DP Level Transmitter

08/28/2012 12:33 AM

It may depend whether low/high refers to liquid level, or pressure. (Since the higher pressure occurs at the lower level, and vice versa.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#4

Re: DP Level Transmitter

08/28/2012 9:14 AM

In "dry leg" systems where the gas pressure compensating line contains no liquid, the transmitter's "H" port is connected to the bottom tap and the "L" port to the top tap. Since the dry leg sees nothing but gas pressure while the wet leg sees gas pressure plus hydrostatic pressure of the liquid inside the vessel, the "H" side pressure will always be greater than the "L" side pressure, and this pressure difference increases as liquid level increases.

In "wet leg" systems where the gas pressure compensating line is filled full with liquid, it is traditional to connect the transmitter's "H" port to the top tap and the "L" port to the bottom tap. The reason for this has to do with the construction of legacy force-balance DP transmitters, many models of which were unable to measure large negative differences in pressure (i.e. where the "L" pressure was significantly greater than the "H" pressure). Since the wet leg connected to the top tap is guaranteed to have its full height always filled with liquid, but the low-side tap sees a varying liquid level, the DP transmitter's connection to the top tap will always see a greater hydrostatic pressure than the bottom tap connection. Therefore, old-style DP transmitters were connected "backwards" with the "H" port connected to the top tap in order to ensure the "H" pressure was always greater than the "L" pressure. This also meant the transmitter was "reverse indicating:" greater liquid level in the vessel created greater pressure at the bottom tap (greater pressure at the transmitter's "L" port), causing the transmitter to output a decreased signal.

With the advent of electronic DP transmitters capable of measuring positive and negative differential pressures with equal accuracy, there is no longer a need to connect the "H" port to the top and the "L" port to the bottom in wet-leg service. However, there are so many engineers and technicians accustomed to traditional installation standards, we often see the "reverse" convention ("H" to top, "L" to bottom) still applied.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Reply Score 1 for Good Answer
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#5

Re: DP Level Transmitter

08/28/2012 3:14 PM

Friend,

A good point regarding this issue is that if you use H side (bottom) and L side (top) you will need use negative range in order to measure the level for example LRV: -150"H2O and URV: -10"H2O, and if you invert the taps, I mean H side (top) and L side (bottom) you will need use positive range for example LRV: 200"H2O and URV: 50"H2O, Whatever you selected the transmitter can be able to measure level the important thing is know how to calculate the range in order to get a correct 4-20mA relation according level decreasing/increasing.

Just remember this: Dp = H - L, the transmitter executed this function.

Few days ago I readed some article about vacuum application using Delta pressure level transmitter but I dont remember very good the recommendations

Regards
JP

__________________
Instruments-guy-SAV
Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Instruments-guy-SAV (1); Joshi (1); metalSmiths (1); tonykuphaldt (1); Tornado (1)

Previous in Forum: Control Valve   Next in Forum: Opening/Closing Time - Control Valves & On-Off Valves

Advertisement