Consider that a control valve is operated through siemens positioner ps2......From DCS i am giving 20% open....i could get 20% in positioner....My question is how does positioner knows that valve is open 20%.....from where it gets its feedback.........
Good Answers: 104
Re: Control Valve
08/27/2012 12:38 PM
On this diagram (from the Siemens PS2 site) down near the bottom you will see a dashed line from the actuator (labeled 'travel'). This provides positionl feedback to the positioner. I'm not familiar with Siemens specifically, but the positioners I've used have a mechanical connection to the valve (or actuator output) that provides this feedback. Somewhere there has to be a physical (mechanical or electrical) connection to do this. Shouldn't be too hard to figure out. Attach a picture if you still can't figure it out.
Re: Control Valve
08/28/2012 4:41 AM
Thanks for ur information....
Good Answers: 176
Re: Control Valve
08/27/2012 12:58 PM
It's always a good idea to start with the manual, because many times, there are even illustrations, like the hardware for mounting to a linear actuator, as shown below:
Good Answers: 266
Re: Control Valve
08/27/2012 1:43 PM
Feed back from linear or rotary encoder depending on the type of valve. Changes in the count in the programing corresponding to what percentage the valve is open.
Re: Control Valve
08/28/2012 4:28 AM
All the above is fine though it pays to remember one is not trying to control valve position, for that is the positioner unit's job. Actually, one is trying to get the process variable to achieve the setpoint.