NGR Closing of Multiple Generator

09/04/2012 3:46 AM

We have 02 generator 26MVA each.Normally both are in operation and synchronized. 100 A , 63.5 Ω NGR's are installed in each generator . Our scheme is

  • NGR of one GTG is closed.
  • In case of grounf fault when GTG (whose NGR is closed) is tripped NGR is opened.
  • system becomes ungrounded.

In above scheme problem is when system is ungrounded , voltage does not remain stable and other GTG also trips on Over-voltage.

We are proposing to Close both NGR's when both GTG's are in operation.both This will create a problem that both GTG's will be tripped in case of ground fault.

which scheme we should adopt , what is recommended practice , what are pros and cons of both schemes.

Register to Reply
Pathfinder Tags: grounding NGR
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: NGR closing of Multiple generator

09/04/2012 5:11 AM

Each individual GTG should be protected by its own NGR, at all times. Is this a new installation. Obviously, the system had performed in the past. The unbalanced GTG is not able to clear unbalance effectively, fast enough.

Register to Reply
Member

Join Date: Sep 2012
Posts: 5
#2
In reply to #1

Re: NGR closing of Multiple generator

09/04/2012 5:45 AM

If Both NGR's are closed fault current will flow in both GTG's and we will have to face blackout.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: NGR closing of Multiple generator

09/04/2012 5:47 AM

Don't do it, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: NGR closing of Multiple generator

09/04/2012 5:48 AM

Voltage of what in reference to what?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Sep 2012
Posts: 5
#5
In reply to #4

Re: NGR closing of Multiple generator

09/04/2012 5:51 AM

Generator Voltage which is 11 KV L-L

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: NGR closing of Multiple generator

09/04/2012 7:25 AM

How does the 11kV L-L vary when the trip has operated?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Sep 2012
Posts: 5
#8
In reply to #7

Re: NGR closing of Multiple generator

09/04/2012 7:28 AM

When one generator has trippped , voltage of other generator whose NGR is opened varies

Register to Reply
Member

Join Date: May 2008
Location: Kuala Lumpur
Posts: 6
#6

Re: NGR closing of Multiple generator

09/04/2012 6:31 AM

A Bakar,

Assuming your generator rated full load current is higher than the maximum allowable earth-fault current (100A in your case), can you kindly explain why the need to trip the generator immediately? What anticipated damage are you preventing here?

Register to Reply
Member

Join Date: Sep 2012
Posts: 5
#9
In reply to #6

Re: NGR closing of Multiple generator

09/04/2012 7:31 AM

Generator is notbeing tripped immediately we have 51GN protection . i need what is recommended pratice in such type of power systems and what are pros and cons of both schemes.

We have to trip generator on earth fault to avoid core damage

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #9

Re: NGR closing of Multiple generator

09/04/2012 10:35 AM

Pl. go for bus earthing with Zig-Zag Transformer & NGR. Once both the generators are synchronised, bring bus earthing on-line & open both the NGRs. Thus, the system will be grounded and the generators wouldn't be. This would solve many problems.

Register to Reply
Member

Join Date: May 2008
Location: Kuala Lumpur
Posts: 6
#11

Re: NGR Closing of Multiple Generator

09/05/2012 4:50 AM

It is a normal practice also to earth (in this case via NGR) all generators in operation. However, the requiremnt with this method is that you have to set the GF setting at the 11kV downstream consumer reference to the sum of all the NGR rated current. If one day you decide to run with only one generator, while the other generator on maintenance, due to safety you have to disconnect the NGR for that off-service generator, and re-configure the GF current setting again at the consumers.

Also if one day your company decides to expand by adding more generators, you have to reconfigure them yet again.

One way to avoid this is by introducing neutral-earthing transformer to your 11kV system, and reduce the NGR rating connected to your genset to say 5A (which is more forgiving to your core insulation)

It sounds to me from your posting that this earth-fault occurs within the core windings. If it occurs elsewhere downstream gen terminal, it should have been cleared by other protection e.g. differential prot, and 51G at consumers.

Having said that, I can't understand why both generators will trip when both are grounded, because it's very unlikely both genset to have internal faults simultaneously (unless you set them on instantaneous trip - which you already said no).

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#12

Re: NGR Closing of Multiple Generator

09/05/2012 12:47 PM

Not sure what your generator winding configuration is: "WYE" or "DELTA" ?

If "WYE" configured and you lift/unground the star point (wye point);

The "B" phase voltage will definitely become unstable. ("Wild-leg" condition)

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abu Bakar (4); electricalexpert65 (1); Joshi (1); NAMINI (2); PWSlack (3); SHOCKISCAN (1)