Can anybody list out what are the releases in MCCB circuit breaker?
Pathfinder Tags: Releases in circuit breaker
Re: Releases in circuit breaker
09/08/2012 4:08 AM
Yes, Guv. Anybody can do this because the ratings are on a permanently-attached label on the front of the breaker.
Good moaning!
Good Answers: 181
09/08/2012 7:46 AM
Re: Releases in Circuit Breaker
09/09/2012 1:31 AM
No Need to put Circuit Breaker after MCCB (Moulded Case Circuit Breaker)
[1] Over Current Release for O/L & Short Circuit Protection
It May be Thermo-Magnetic or Microprocessor based as well.uP based will/may offer Earth Fault Protection also.
[2] Shut Release (or Trip Coil) for Electrically Tripping the MCCB
[3] Under Voltage Release for No Volt Protection
Good Answers: 170
09/09/2012 9:40 AM
Thermal-Magnetic:
Over-current (Time-delayed) & Short-Circuit (Instantaneous)
with optional add-on external earth fault release
Micro-processor based:
Over-current with time delay (long-time pick-up & time delay)
Short-circuit with time delay (short-time pick-up & time delay) with limits on current setting & on time setting (limited by the short time withstand capacity of the MCCB)
Short-circuit Instantaneous (Instantaneous): To over-ride the Short Time Pick-up release, if the fault current is beyond the setting made in this instantaneous release
Ground-fault with time delay (Ground fault Pick-up & time delay)
Ground fault Instantaneous
I2t ON/OFF
Thermal Reflectivity ON/OFF
Thermal Memory ON/OFF
Instantaneous Doubling (Cold load Pick up ON/OFF)
Under voltage Release
Shunt Release
France - Member - New Member
09/10/2012 4:18 AM
It depends completely on the trip unit that is fitted on the MCCB ... can vary from basic up to the most sophisticated . I advise to check on the existing CB, if this is your case, or to write your need on the spec you issue, if this is your case .