can anybody list out what are the fault relay protection needed for motor protections
Pathfinder Tags: Motor Protection
Re: relay protection for motor
09/08/2012 4:07 AM
Yes, Guv. Anybody can do this when they see the motor rating plate, because the full load current is stamped onto the plate.
Good moaning!
Good Answers: 181
09/08/2012 7:50 AM
Sorry the homework answering sevice is off line.
Re: Relay Protection for Motor
09/09/2012 1:25 AM
OC,SC,EF,phase reversal,phase unbalance,phase failure,winding temperature,under-current,bearing temperature etc depending on the rating of the motor.
pnaban
Good Answers: 170
09/09/2012 9:31 AM
It depnds upon many factors.
MOTOR PROTECTION - How Much Protection is enough?
The answer depends on:
Rewinding Cost
Loss of Production
Effect on Downtime
New versus old installation
Need for communication
Metering & Control
MOTOR PROTECTION - PRACTICES
Less than 10kW: Bimetal Overload Relay with built-in protection against single-phasing
10kW to 50kW:
Thermal Overload
Over current
Earth fault
Unbalance
Locked Rotor
50kW & above:
Thermal overload
Over current
Earth fault
Locked Rotor
Unbalance
Repeat Starts
Under load
Prolonged Start
Good Answers: 42
09/09/2012 11:53 PM
This is a normal general question which I used to ask candidates coming for job interviews or written tests. You need to study the subject to answer.
Better read the following link .This may help you.
http://www.l-3.com/wp/wp-content/uploads/2010/10/Motor-Protective-Settings1.pdf