OLR Setting

09/08/2012 5:30 AM

dear all

33Amp three phase motor starter . In OLR ( overload relay ) howmach overload current need to set.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: OLR setting

09/08/2012 6:03 AM

Look on the name plate of the motor, for full load current & set your OLR accordingly.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2011
Posts: 4
#2

Re: OLR setting

09/08/2012 8:09 AM

10 % Generally

Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: OLR setting

09/08/2012 11:19 AM

Oops, wrong answer. No 10% or any other factor is applicable.

Joshi's answer is correct, you should set it at the rated current of the motor (if it is a DOL starter and the FLA is passing through it).

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: OLR setting

09/08/2012 10:27 PM

Not quite. If the OLR is in a different ambient temperature location from the motor, some adjustments may be appropriate. With fixed heaters, this can mean a size or two up or down. With adjustable relays, this may mean ± some similar amount. One case of special interest is fan motors in blast freezers at -35°C. The extra cold air can allow actual amps to be something like 20% above normal FLC.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #4

Re: OLR setting

09/09/2012 7:19 AM

Most IEC devices available in India are ambient-compensated. In fact the good ones are "under-compensated" by 0.4% per °C to take into account the difference in thermal mass between the OLR and the motor. US-style eutectic alloy relays are not ambient compensated as you rightly point out.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #6

Re: OLR setting

09/09/2012 10:34 AM

I see how an ORL can be ambient-compensated for its own ambient, but not for the motor's ambient if different. The IEC doesn't address this?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#11
In reply to #10

Re: OLR setting

09/09/2012 10:47 AM

Please revisit #6

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #11

Re: OLR setting

09/09/2012 4:31 PM

Irrelevant. I am not talking about the thermal mass of the motor; I am talking about quite different ambient temperatures at the OLR versus the motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #10

Re: OLR setting

09/09/2012 11:19 AM

i believe it does. Hence the under-compensation, which actually is implied in IEC 60947-4 vide this figure...

The non-trip/trip gates are 1.05/1.2 at 20°C, and 1.00/1.2 @ 40°C. This, to me, allows for the higher thermal mass of the motor. If the relay wasn't ambient-compensated, it would trip unnecessarily at a lower current, over-protecting the motor. i do believe that the ambient compensation is actually to prevent nuisance tripping of the relay, if they are both at the same ambient. If the relay is in a controlled ambient say 20°C, and the motor is toiling at say 40°C, there may be an unprotected zone (1.00 - 1.05) but this is statistically ignorable in view of the better performance in most other conditions (both at same ambient, motor at different but not too high an ambient, etc). Just my opinion.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#5

Re: OLR Setting

09/09/2012 6:36 AM

+20% of FLC is acceptable for c class insulation. also you have to mind the connections

* or D

__________________
love4everyone
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7
In reply to #5

Re: OLR Setting

09/09/2012 9:24 AM

Grossly incorrect! Only Joshi & KVS are correct. The OLR must be set to - not more than - the rated full load current of the motor. However, one can set the OLR to less than the FLC of the motor, if the motor is oversized.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: OLR Setting

09/09/2012 9:56 AM

RTFM.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#9
In reply to #8

Re: OLR Setting

09/09/2012 10:12 AM

The MANUAL is not always, the gospel truth. There are always exceptions to that.

Register to Reply Off Topic (Score 6)
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#14

Re: OLR Setting

09/09/2012 4:57 PM

You can set the overload to whatever you want, but if you set it to more than FLA you are going to shorten the life of the motor if it runs above FLA.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #14

Re: OLR Setting

09/09/2012 7:15 PM

Not necessarily, as in the blast freezer fans described previously.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#16

OLR Setting

09/10/2012 7:35 AM

refer

Table 430-148 (From 1999 NEC) or

Table 430-150 (From 1999 NEC)

Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); electricalexpert65 (1); eltech (1); Joshi (1); karanthsp (1); kvsridhar (3); Muthuvel (1); sohail0110 (1); Tornado (5)