Neutral Size Compared to Phases

09/08/2012 8:13 AM

In3ph 4wire systemNeutralis always rate 1/2 of main.Any standard available against this???

Register to Reply
Pathfinder Tags: Neutral Bus size
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Neutral Size compared to Phases.

09/08/2012 1:05 PM

Who say's it's always ½ the rating of the main conductor?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Neutral Size Compared to Phases

09/08/2012 4:45 PM

Yes. It depends on the possibilities of phase imbalance and presence of harmonics, for instance.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Neutral Size Compared to Phases

09/08/2012 5:45 PM

I agree with T and T. if you have a high harmonic load, the neutral may be larger than the phase conductors. The other factor is how well the load is balanced.

Check these sites for additional information

http://www.electrical-installation.org/enwiki/Sizing_the_neutral_conductor

http://www.tlc-direct.co.uk/Book/4.3.12.htm

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Neutral Size Compared to Phases

09/09/2012 9:21 AM

Not "ALWAYS". It depends largely on the distribution and/or utilisation of single-phase loads distributed on to three phases. Under the worst conditions, it could just be possible that only one of the three phases could be loaded to full capacity with the other two phases unloade, in which case, the neutral MUST be sized equal to the phase.

And.... even that is not enough today. Today, with the advent of power electronics, one needs to even 'double-size' the neutral (i.e.) the size (cross sectiona area) of the neutral conductor is twice that of the phase conductor, thanks to triplen harmonics.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); TonyS (1); Tornado (1); wareagle (1)

Previous in Forum: OLR Setting   Next in Forum: Grounding Electrical Meter

Advertisement