Thumb Rules of Refrigeration?
09/10/2012 12:53 PM
What are the Thumb Rules of Refrigeration?
What is the relationship between Compressor Capacity(TR) and Cooling Surface of Condenser/Chiller?
What is the relation between Compressor Capacity(TR) and Motor HP/KW?
How the sizing is done?
U.M.Patankar
Re: Thumbs Rules of Refrigeration?
09/10/2012 1:05 PM
Re: Thumb Rules of Refrigeration?
09/11/2012 2:05 AM
None of the above.
Try a new multiple-choice test.
Good Answers: 67
09/29/2012 7:14 AM
Uday, first of all compressor capacity is not TR. Also Compressor Capacity can not be compared with Cooling Surface which is area.
Here I want to explain very simple fundamentals. Divide the cooling capacity of chiller expressed in kcal/hr by 3000 to get TR. Now about the relationship among terms in your question is as follows:
Cooling capacity of condenser = Cooling capacity of chiller + compressor power (in heat units)
Above relationship can be easily verifiable in PH diagram (no thumb rule). Also a very important performance parameter (COP) is derived from the two terms on RHS.
COP = Cooling capacity of chiller / compressor power (in heat units)
09/30/2012 1:47 AM
Dear Mr. Pritam,
Thanks.
U.M.Patankar