ESP Air Leak Test, Boiler Duct Air Leak Test

09/10/2012 8:46 AM

I would like to know the criticality/importance of ESP air leak test and Boiler duct air leak test in thermal power plants.

Nowadays these tests are not being done in some of the Projects by EXECUTION/ERECTION depts to save time, by doing simple kerosin tests etc which are not substitute for air leak teast with blower/fan.

What are the affects in operation of Boilers operation if the leaks are more?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ESP Air Leak Test, Boiler Duct Air Leak Test

09/10/2012 10:27 AM

If the facility hasn't got time to do it properly, where is it going to find the time from to put it right after it has gone wrong?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#2

Re: ESP Air Leak Test, Boiler Duct Air Leak Test

09/10/2012 11:02 AM

Nowadays these tests are not being done in some of the Projects by EXECUTION/ERECTION depts to save time. Why are you being bothered then. Let them find out the hard way after commissioning.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: ESP Air Leak Test, Boiler Duct Air Leak Test

09/10/2012 11:06 AM

"What are the affects in operation of Boilers operation if the leaks are more?"

Overall efficiency of the boiler will suffer.

Register to Reply
Active Contributor

Join Date: Oct 2012
Posts: 10
#4
In reply to #3

Re: ESP Air Leak Test, Boiler Duct Air Leak Test

10/25/2012 2:39 AM

Duct and flue leaks reduce efficiency and cost money. The time to test for leaks is after the fabrication (diesel testing) and erection (smoke testing) of the equipment. Diesel testing is a bit messy but effective as diesel will leak through vey small perosity weld leaks. Smoke testing is difficult as you have to isolate each section of duct and apply a small pressure, perhaps 20 mbar. If the ducts are diesel tested during fabrication it is possible to insulate most of the duct leaving only field welded joints for smoke test. In this thread it is stated that much of the time no tests are done on-site and I suspect this is because it is late in the project and everyone is revved up to complete ASAP. Infrared testing can only be done during operation.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: ESP Air Leak Test, Boiler Duct Air Leak Test

02/09/2013 11:41 AM

Dear Mr.csrao

The test referred by you is a must and compulsorily to be done. Question of Saving of Time is not the right argument. On the other hand, it is worth to conduct these test - even if it is delayed.

The bad effects of LEAKAGE in the duct are : 1. Insufficient air at the Furnace, since the leakage results in short-circuit of air flow, thus reducing the air quantity at the furnace. 2. Higher chances for incomplete combustion and formation of CO, thus Heat Loss. 3. Leaky air, will lower the Flue Gas Temp. and may fall below the DEW-POINT Temp. thus condensation of water will start and damage the ID Fan Impeller. 4. Due to leakage, Flue Gas Temp. will fall and reduce the Natural Draught available.

DHAYANANDHAN.S

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); dsmith (1); ducon (1); Joshi (1); PWSlack (1)