Sizing of Neutral Earthing Strip

09/11/2012 3:01 AM

How to size the neutral earthing strip and number of earth pit for neutral earthing

ie)for example exercise 500kVA,430V power system

Register to Reply
Pathfinder Tags: Neutral earth strip size
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Sizing of neutral earthing strip.

09/11/2012 3:12 AM

One of the ways is to follow British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - Lifelong New Yorker Popular Science - Biology - Animal Science Technical Fields - Technical Writing - Technical Writer

Join Date: Mar 2008
Location: NY
Posts: 2313
Good Answers: 59
#2

Re: Sizing of Neutral Earthing Strip

09/11/2012 7:15 AM

Try searching on CR4 - this question has been asked several times.

CR4 search: neutral earthing strip

Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#3
In reply to #2

Re: Sizing of Neutral Earthing Strip

09/11/2012 7:46 AM

In CR4 there is no discussion for Neutral earth strip calculation.

The discussions what they did is only for body earthing strip calculations.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Sizing of Neutral Earthing Strip

09/11/2012 10:02 AM

For 500kVA Transformer, the recommended Earth Strip Size for Neutral Earthing is:

i) 25mm x 6mm Bare Copper Strip

or

ii) 300 sq.mm PVC Insulated Aluminium Conductor

or

iii) 50mm x 6mm GI Strip

Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#6
In reply to #4

Sizing of Neutral Earthing Strip

09/12/2012 12:47 AM

I know as per IS3043-1965 Annexure-D 25X6mm Cu strip or 300sq.mm Al Con

is recommended but I am asking the formula to Calculate the size .

I know the formula to size the body earthing meanwhile I need to know

formula for neutral earthing.

Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7
In reply to #6

Re: Sizing of Neutral Earthing Strip

09/12/2012 9:26 AM

The Standard IS 3043 does not differentiate between a neutral earthing conductor and a body earthing conductor. As per the Standard, the formula for sizing earthing conductors & protective conductors is:

S = I Root 't' / K

where,

S is the cross sectional area of the protective conductor in sq.mm

I is the fault current is Amperes

t is the fault duration in seconds

K is the Adiabatic Constant depending upon the Material of the conductor, method of laying, etc. (given vide Table 6 of IS 3043).

By the by do not refer to IS 3043-1965.

This has been revised in 1987 and amended latest in january 2010.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Sizing of Neutral Earthing Strip

09/11/2012 6:49 PM

As this is only an exercise does it realy matter?

You should do you're own research. You will learn so much more that constantly coming to CR4 to be given the answers. But you have been told this before.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 7 comments