Problem In Gas Supervision Contractor of 66KV SF6 Breaker Make ABB

09/11/2012 10:10 AM

hi every body,i have a problem iam working in 132/66kv grid station ,i have a breaker installed in 66 KV side its gas supervision contractor is not operating although the gas in the breaker is up to the required level (.72Mpa), where the required level is .62Mpa. please tell me what is the problem, it is very urgent

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: problem in gas supervision contractor of 66KV SF6 breaker make ABB

09/11/2012 10:17 AM

The problem seems to be one of not telephoning the breaker manufacturer's technical helpline for advice and support.

  • Has this thing been bench tested?
  • Or set-up by the manufacturer's roving technician at some point?
  • Has the panel been through cFAT before being shipped to site?
  • Etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: problem in gas supervision contractor of 66KV SF6 breaker make ABB

09/11/2012 11:15 AM

How do you know that the gas supervision contactor is not working? Are you assuming that because one gauge is showing the right pressure that the pressure is actually correct? Suppose the gauge is stuck and the pressure switch is correct in reporting low pressure.

I am going to assume that this contactor is not picking up and is therefore preventing the breaker form closing due to low gas pressure. The first thing that you need to do is lock out the breaker by removing all control power so that it doesn't accidently close while you are servicing it. Next you need an independent calibrated gauge hooked up to another test point to verify that the gas is indeed at the right pressure. If it is then you need find the pressure transducer/switch that provides the go/no-go signal to the control logic that feeds the contactor. Check to see that it is reporting the correct pressure, if not find out why. If it is then you need to check the contactor coil for continuity, if it is ok then ensure that all permissive contacts are operating correctly.

If you do not understand or know how to perform any of these steps then put your hands in your pockets, walk away from the equipment, call the manufacturer and wait for qualified help. An SF-6 breaker that is energized or closed with an inadequate gas supply/pressure will most likely be permanently damaged, as will any personnel in the immediate area, that's why there are so many fail-safe mechanisms and controls built in to it.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #2

Re: problem in gas supervision contractor of 66KV SF6 breaker make ABB

09/11/2012 3:07 PM

Excellent reply. Worth a GA point from me.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".