Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/12/2012 12:46 PM

What is the reason of over heating(red hot with in one min.) of neutral earthing of 1500 kVA DG Set ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#1

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/12/2012 1:55 PM

Insufficient current carrying capacity would be my guess.

A more important question would be, why is this current going to ground.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/12/2012 2:33 PM

My first concern would be to find out how much current is being carried on neutral earthing circuit and find out where its coming from!

Is one phase grossly overloaded or is there a partial short in a the generator windings or another device that shares a common earth ground point creating a high current short circuit?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/12/2012 11:28 PM

Short answer is there is current flowing in that conductor.

Is this with or without a load?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 12:21 AM

The CB should trip before conductor attains high temperature for prolonged period.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #4

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 1:08 AM

Looks like it is stuck!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#6
In reply to #4

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 3:11 AM

If the neutral strip is getting this hot, it is unlikely that the installation is wired correctly, and unlikely that the correct circuit breaker has been provided, if any has been provided at all.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#14
In reply to #4

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 8:14 PM

The OP did not state whether this is a newly developed condition or if the issue has been present since DG system inception/installation which is extremely important for analyzing the cause.

I have not yet observed a neutral earthing strip routed through a circuit breaker on a DG or any other generator.

The amount of current present on the earthing ground is dependent on system design and actual wiring configuration.

Tripping of the load circuit brreaker would depend on how the system is wired, and whether there is active, properly sized ground fault protection present in the generator protection circuitry.

Use a clamp on non-contact ammeter to measure the amount/magnitude of current flowing throught the neutral earthing strip.

Verify the wiring and if correctly connected/configured, determine the allowable magnitude of current on the neutral earthing strip as per design.

If the measured value is within acceptable design value but greater than the rating of the existing neutral earthing strip size allows, replace the strip with the proper sized strip.

If the strip is correctly sized for the application and the measured current value is greater than design allows, check the field wiring for ground/neutral fault conditions and repair.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#7

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 3:12 AM

The reason is that the installation has been assembled incorrectly. De-energise it and consult a qualified electrician to sort it out before someone gets hurt/killed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#8
In reply to #7

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 3:16 AM

It must have melted away by now.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#9
In reply to #8

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 3:40 AM

Then so will the original poster and this thread.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#10
In reply to #9

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 5:07 AM

But where is he?

chandrakant vishwakarma, are you there?

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11
In reply to #10

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 5:26 AM

Give the fella at least 24 hrs to check and respond to his personal email....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#15
In reply to #9

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/15/2012 7:57 PM

The inevitable, I am afraid, has finally happened.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#12

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 8:05 AM

Incorrect installation.Check also the size of the neutral conductor

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#13

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/13/2012 11:55 AM

To generate heat you need a resistance. Everything tells me its likely this DG set has a large single phase load attached to it and that its on a grubby site and needs some tender loving care. I don't know what voltage the set is at but likely there is 100 ish amps going back on the neutral. Even if you have a half an Ohm resistance at the point of connection you have enough to generate 5kW of heat. Exactly how many Watts do you need to make this bar glow?

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#16

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/17/2012 3:45 AM

In addition of all observations, OP must check the Third Harmonic components of the system.

Manindra.

__________________
Manindra
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#17
In reply to #16

Re: Over Heating of Neutral Earthing Strip of 1500kVA DG Set.

09/17/2012 6:20 AM

Unlikely to be an issue. The neutral of the cable would be red hot.

If it was an issue I can't see it being as spectacular or fast as is suggested.

If the set is only loaded to about 75% the triplen harmonics won't be an issue anyway.

This sounds like localised heat and a bad/dirty/undersized connection to the bar.

Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Joshi (4); lyn (1); manindra (1); nesubra (1); pnaban (1); PWSlack (3); SHOCKISCAN (1); silverfox (2); tcmtech (1); Wal (2)