Flooded AHU

09/18/2012 5:08 AM

We have many chilled water AHU with different sizes and different cooling capacities, some of them reserves condensed moisture outside water condensation pan where no drain line, it results for more water accumulation around blower area, it becomes full and results for water floods outside the unit through side walls and spilled on the surrounding floor

My questions, why some units like that while all others collect and drain water through the ordinary drain line for water condensation pan.

thanks in advance

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: flooded AHU

09/18/2012 5:14 AM

The absence of an intended drain line, a leak or a blockage in the one that is installed are all possible causes of a problem like this. One must expect air cooling equipment to have a water waste stream, and install and maintain a suitable waste pipe accordingly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#3
In reply to #1

Re: flooded AHU

09/18/2012 5:37 AM

There is already a drain line which is connected to condensed water pan and located under chilled water coil , also it's clear and works good.

the problem is the water which condensed out side condensation drain pan

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: flooded AHU

09/18/2012 6:04 AM

Apply thermal insulation lagging to the equipment. Something that is waterproof will do fine. Outside moist air is coming into contact with cold surfaces and condensing on them. Lagging will reduce or prevent this from happening.

Lagging will also reduce the equipment's power requirements slightly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#6
In reply to #4

Re: flooded AHU

09/18/2012 6:35 AM

the units are already isolated with double wall and thermal isolation in between.

no condense water at outside walls. but water comes from unit inside

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #6

Re: flooded AHU

09/18/2012 8:50 AM

Is there anything else that the forum needs to know?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: flooded AHU

09/18/2012 5:16 AM

Consider providing proper drainage to overcome flooding & it's related problems.

Register to Reply
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#5
In reply to #2

Re: flooded AHU

09/18/2012 6:23 AM

you are right. it's an easy solution .

but i would like to know why water leaves or skip condensing pan and accumulates outside in blower area

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
2
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#7
In reply to #5

Re: flooded AHU

09/18/2012 7:02 AM

Are you saying the condensation formed on the coil is not being caught by the pan? In other words, it is being blown past the pan? If so, it could be due to excess air flow velocity or a dirty coil.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#8
In reply to #7

Re: flooded AHU

09/18/2012 7:30 AM

Dear bigg.

you are demonstrating our problem better than me. it's the right case we are facing.

are there any other probabilities for this issue


GA from me

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #8

Re: flooded AHU

09/18/2012 5:47 PM

This can be caused by oil residue on the coil causing the water to bead instead of clinging to the fins....Try spraying some low sudsing soap on the coil to increase the surfactant quality....This might take a few treatments...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#15
In reply to #10

Re: flooded AHU

09/19/2012 2:32 AM

good suggestion and easy treatment

thank you

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Participant

Join Date: Sep 2012
Posts: 4
#14
In reply to #8

Re: flooded AHU

09/19/2012 2:23 AM

The most important is stopping the condensate from the coil to occur, the fan has nothing to do with the source of the problems. take a second look into the chilled water flow rate, entering and leaving temperature of the coil. Once these parameters are properly adjusted, hence we will have the problem solved.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#11

Re: Flooded AHU

09/18/2012 11:27 PM

The suggestion regarding a dirty coil is a possibility BUT- make sure that the chilled water is flowing at the proper rate.

This is a wild guess, but- if flow is low, almost ALL of the moisture removal will come from the last row or two of the coils, rather than about two-thirds of it. The easiest way to check flow is entering and leaving temperatures.

Check the specified temperature difference for the coils- it should be around 5 to 8.5C differential with entering temp around 6C to 8C entering. If you are looking at leaving water temp of 16C or warmer, you have low flow and nearly all of the cooling (and moisture removal) is happening in the final coil or two, triggering over-spray because it is flooding the face.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#16
In reply to #11

Re: Flooded AHU

09/19/2012 2:45 AM

Dear energygod

you are a real Veteran guru

GA for U

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Participant

Join Date: Sep 2012
Posts: 4
#12

Re: Flooded AHU

09/19/2012 1:17 AM

Check for blockage in the condensate drain line. It is very possible that all the AHUs experiencing this flooding; the drain pipes are connected together.

Register to Reply
Participant

Join Date: Sep 2012
Location: caberra
Posts: 1
#13
In reply to #12

Re: Flooded AHU

09/19/2012 2:01 AM

Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#17

Re: Flooded AHU

09/19/2012 11:51 AM

It could be a case of dirty / blocked coil. The fan is partially sucking air through the coil and because the coils are dirty the excess air is sucked from the condenstate pan through the connecting drain pipe line resulting in floods at the motor drive side.This eventually flows out and floods the area.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#19
In reply to #17

Re: Flooded AHU

09/20/2012 2:04 AM

Dear pillay

very logical conception and GA

thank you

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#18

Re: Flooded AHU

09/19/2012 4:13 PM

Hi khairy: A couple of situations can cause the pan to not drain properly.

Start with the more common cause, a clogged drain line or an obstruction over the drain pan opening.

If neither of these is a culprit give a holler and I can furnish you more complicated suggestions..

Good luck.

Lou Bindner

Register to Reply
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#20
In reply to #18

Re: Flooded AHU

09/20/2012 2:16 AM

Dear Binder

Drain line is not clogged. Waiting your complicating suggestion

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#21

Re: Flooded AHU

09/20/2012 4:04 AM

I am thinking about U Trap condition for condensation draining line ........ We have face similar problem and fault is with the U-trap .......

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2007
Posts: 142
Good Answers: 1
#22

Re: Flooded AHU

11/29/2012 4:53 PM

This sounds like a trap depth problem on the drain itself.

Their are typically minimum distances for trap depth as it relates to the design air flow velocities. That distance is found in the installation manual and on Trane, Mcquay & Carrier units its posted to the units. It depends on the inches of water velocity of the air flow.

The reason it may be occurring on some and not others may have to do with the fan speeds occurring on some of the units.

This can be a big problem especially if the unts are not elevated on rails or housekeeping pads, limiting the distance on the trap depth.

Register to Reply Off Topic (Score 5)
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Babs (2); bashir01219 (1); batteriesshop40 (1); bigg (1); energygod (1); Joshi (1); khairy Aish (8); Lou Bindner (1); pillay (1); pipeit (1); PWSlack (3); SolarEagle (1)

Previous in Forum: Compressed Air Consumption Calculation   Next in Forum: Coated Nuts & Bolts - Repair with Polyurethane Paint?

Advertisement