Question:
The nameplate on a 50 kVA transformer shows a primary voltage of 480 V and a secondary voltage of 120 V.We wish to determine the approximate number of turns on the primary and secondary windings. Toward this end, three turns of wire are wound around the external winding, and a voltmeter is connected across the 3-turn coil. A voltage of 76 V is then applied to the 120 V winding, and the voltage across the 3-turn winding is found to be 0.93 V. How many turns are there on the 480 V and 120 V windings (approximately)?
Answer: With 76 volts applied, the constant is 0.93v/3T = 0.31 V/T.
Correcting that for 120 volts instead of 76, that becomes (0.31 V/T)(120/76) = 0.489 V/T.So the 120 volt winding has 120 V / 0.489 V/T = 245 turns
the 480 would have 4 times as many or 980 turns.
I really want to understand this question,the answer what my instructor told me is given up but he said you can use another approach to solve this question by using primary and secondary voltages and turns ratio.I dunt want to use V/T method and i wanna try other one out cuz my next test will be from other approach, i cant undertand thi part "A voltage of 76 V is then applied to the 120 V winding, and the voltage across the 3-turn winding is found to be 0.93 V".I donot know what voltage we have to use for secondary winding 120V or 76V.And can i find some voltages or current from power rating of transformer?
Any solutions or suggetions will be greatly helpful.Sorry for long thread but i m new to this forum and donot know much how to communicate effectively(any suggesstions to short up my thread will also be helpful).Thank you very very much for your time.