Soft Start?

09/20/2012 1:27 PM

Have an infrared oven with 57k + watts in it. Has 36 240 v 1600k watt lamps. Zoned out with 12 lamps to a zone. The zones work off sensors to product size linearly across the oven entrance. The 12 lamps are powered by one mechanical contactor. With a 3 phase 480 volt input the lamps ran in series. Two delta configuration circuits with 6 lamps on each. One circuit to the top and one to the bottom of the oven. There is no temperature control. The heat up time is controlled by how fast the product is conveyed through the oven. Switch on by sensors as the products conveyed through and shut down by timers.

I had thought about thermistor but the duration of 40 sec may not give them time to cool down.

The OEM used mechanical contactor and they do not hold up well. They were not much help when I addressed it with then.

Would a soft starter handle a resistance load and work in this application?

In looking at the many soft starters available there is not much if anything about resistant load capabilities.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Soft Start?

09/20/2012 1:55 PM

"The OEM used mechanical contactor and they do not hold up well"

Use solid state relay instead.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Soft Start?

09/20/2012 2:19 PM

The term "Soft Start" is a motor control device, they typically don't provide info on resistive applications because it is often done differently for that application, The same type of device for resistive loads is called an "SCR Power Controller". Different manufacturers, and there are several other design considerations regarding that. Contact people in the heating control industry.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#3

Re: Soft Start?

09/21/2012 4:20 AM

You generally use a soft start to limit the inrush current of an inductive device such as a large motor. You have a resistive load so will not have the same issues.

Suggest you replace the contactor but instead of going for an AC1 rated device you could go for a more substantial AC3. kW rating would be the same but made for much more onerous duty cycle.

Using a soft start might help to increase to increase lamp life by limiting the current.

You will still need a contactor to bypass around the soft start after 30 secs (ish) to reduce losses.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4
In reply to #3

Re: Soft Start?

09/21/2012 8:18 AM

These Quartz Halogen lamps have a large inrush current 8 to 14 times the operational current.

Yes the increase in lamp life was a noted benefit. But not because of reduced current. Lamp life increase due to reduced stress on the element.

Some of the soft starters that I was looking at had internal bypass.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Soft Start?

09/21/2012 9:03 AM

OK I'm with the program now.

The "inrush" current you mentioned is due to the filament being cold when it is first turned on. The cold resistance is very low.

In studio lighting applications, where nkW lights are turning on and off with gay abandon, the lamps are never turned off completely. Some current is always passed through them even when not illuminated to keep them warm/hot so that the lamps don't pop prematurely and they can also be quickly modulated in intensity (eg flashed).

Studio lighting is normally controlled with a dimmer pack with DMX control. Easy to set up this way but if you don't need this sort of control you could emulate the preheat function with external resistors paralleled across the contacts of your control device (contactor).

When the contacts are open the current flows through the resistor in series with the lamp and when the contacts close you get full voltage across the lamp and they illuminate at full intensity.

Inefficient for sure. High power resistors required...yes. You could use ordinary lamps for the high powered resistors at a pinch.

Dimmer packs have all this functionality built in and also provide multi channel controlability. They also operate standalone without DMX. They use Triacs.

I think semiconductor control is what you need here.

What was the mode of failure for your contactors? Burnt coils or fried contacts?

Does this help?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#6
In reply to #5

Re: Soft Start?

09/21/2012 11:59 AM

Burnt contacts is the problem. In operation these contactor may open and close 60 times an hour. This varies depending on the size of the product. Smaller sizes are easier worked may be fed into it so frequent the lamps never go off. Large sizes may have it turning off and on 10 times an hour. Not sure contactors were design to open and close that frequently.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Soft Start?

09/21/2012 5:49 PM
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Soft Start?

09/21/2012 11:33 PM

Nice one!

Add that to the library.

__________________
Difficulty is not an obstacle it is merely an attribute.