I am working on the BS and I want to know what the NEC says with regard to the following:
A 3 phase pump motor with full load 20 amps,the manufacturer recommendation is to protect the motor with 40 amps. mccb (with mag. and thermal protection) and starter unit (contactor 30 amps and overload 18-24 amps).
My queries are:
1.will the selected cable size be matching with the circuit breaker size or the motor over load setting?(of course the voltage drop will be considered).
2. BS in their clause for rotating machines say that circuit breakers,starters and cables should be selected to carry not less than motor full load amps. while in some other clause says that Iz should be 1.45 times the circuit breaker size on which the circuit parameters to be selected.