An Alarm for Each PID Controller in DCS

09/27/2012 3:08 AM

Our end user of a refinery insists on having an alarm for each PID controller in DCS. As a newbie, I would provide an alarm only when the P&ID indicates a "HH/H/L/LL". I am confused now since I am of the opinion that alarm is only for alerting the operator. I dont think any action is performed depending on the setpoint.

__________________
If something goes wrong at the plant, blame the guy who can't speak English
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
6
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Hi

09/27/2012 4:02 AM

The need for an alarm on a plant is indicated on the latest "as built" P&ID drawing for the plant. This is because it will have passed through a HazOp Study and the actions from that study will have been completed. The need will also be given in a document called an Alarm Schedule, which is a summary of the alarms indicated on the P&ID that gives the priority of the alarm, the actions of the plant automation and the actions expected of the operatives in response. This document might be stand-alone, or it might form part of a Control Philosophy document written by Process Engineering. Plant automation and procedures need to be set-up and tested against this document, and records of the tests kept in a secure place.

It is unneccessary to provide alarms by initiative beyond this point as these could be classed as nuisance alarms (see the 3 Mile Island incident), though there needs to be a formal HazOp review when any change takes place either to the plant or to what is passing through it.

Putting alarms on setpoints is nonsense; to do so infers that driving the plant into an alarm state is normal accepted practice. Clipping the setpoint so that invalid ones cannot be entered is a much better idea and would be consistent with the principles embraced within the HazOp Study.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 6)
Active Contributor

Join Date: Sep 2012
Location: India / Korea / UAE
Posts: 10
#2
In reply to #1

Re: Hi

09/27/2012 4:14 AM

3 Mile Island Incident is definitely an eye opener.....!

But I still dont understand the mentality of some end users who insist on providing alarms on such controllers, and then blame the EPC/Control System Vendor for generating nuisance alarms .....

__________________
If something goes wrong at the plant, blame the guy who can't speak English
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Hi

09/27/2012 4:17 AM

Refer these users to the approved P&IDs and the HazOp Study report.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2012
Posts: 15
Good Answers: 1
#7
In reply to #1

Re: Hi

09/28/2012 3:35 AM

Agree fully. If you want to get more out of it, I suggest you take a next step and do an Alarm Objective Analysis (AOA) workshop with all the right dudes (and gals) to rationalize all your alarms.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Hi

09/27/2012 7:50 AM

End user you mean the customer. So your going to argue this with them and loose.

He is the customer give him what he wants. Or he may find someone that will.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Hi

09/27/2012 8:32 AM

Determining the need/want is the subject of the HazOp Study.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#6
In reply to #4

Re: Hi

09/27/2012 9:28 AM

OP should be contractually bound to follow customer's (collective) procedures. Said procedures should include hazop, operability studies, etc., conducted with proper representation and documentation. No individual, even an individual customer rep, should have the authority to bypass or negate those. Every project team member should be a gatekeeper.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2012
Location: South Africa
Posts: 13
Good Answers: 3
#8

Re: An Alarm for Each PID Controller in DCS

09/28/2012 7:19 AM

Perhaps they are refering to deviation alarms (standard option in most DCS systems)

This is simply an alarm that will notify the operator if the process deviates more than 10% (assuming the alarm is set at 10%) from the setpoint.

Using this will normally also neccesitate alarm delays - to allow some time for the process to reach the new setpoint in case of adjustment.

__________________
Living is more than mere existence and breath
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9

Re: An Alarm for Each PID Controller in DCS

09/28/2012 8:42 AM

Have you actually received this request from the end user, or is there a big engineering firm in the middle of the job data flow? We often get strange requests on jobs here and comply, only to find out well into the job that the end user did not request this, and indeed does not want this, but rather some green engineer at the engineering firm handling the job put this in the spec package. Then we get to argue over who pays for the unrequired items cost and the cost of the correct items added to the job.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#10

Re: An Alarm for Each PID Controller in DCS

09/28/2012 10:16 AM

There have been some excellent comments placed, and I would like to throw my two cents worth in.

First of all the requirement for alarms for a control or indication is defined during the HAZOP, HAZAN, SIL studies, etc. and the previous experiences from other projects.

These studies will indicate the need for a H, L, H/L, HH, etc.

The function of the H and L settings is generally as an alarm per se, while a HH or LL will generally be used for tripping a safety alarm and shutdown.

Now then what in my limited experience I have found is that in some instances the alarming functions are so overdone, that instead of alerting the operators to an upset condition, they just ignore them due to the fact that there are so many they cannot respond to all.

Based on this I generally suggest that the alarm or trip functions be limited to variables that could have immediate shutdown or hazard results, though it is the process departments decision which signals have what priorities.

When a control room operator gets inundated with dozens to hundreds of alarms its impossible to detect which one is first which one may have higher priorities or even if the alarm was a spurious one. In these cases the operator will generally cancel all the alarms and call either a supervisor or an engineer to have them detect the faults, problems, and potential solutions.

Finally the use of alarms needs to be optimized so instead of an operator silencing them he actual performs corrective actions.

Register to Reply
Associate

Join Date: Jan 2011
Location: Rotorua, New Zealand
Posts: 30
Good Answers: 1
#11

Re: An Alarm for Each PID Controller in DCS

09/30/2012 1:27 AM

Pre microprocessor's, DCS/PLC, alarms were allocated to windows in boxes at a cost of about $140 each. Care was taken in the selection of alarms. Post DCS/PLC we have introduced a situation that has been and will continue to be, a major contributor to industrial process "accidents". Alarm management is generally carried out at the end of a new project. By then the programmers just want to go home, so with the best will in the world the end user is left to carry out this very important activity.

I asked my colleagues a few months ago to give me a report on the amount of alarms received during a 24 hour period at our major coal fired power stations in Australia. You may find this difficult to believe but they averaged out at 79,000 per day!! Some of our major disasters down here, and throughout the world, can be attributed to "alarm swamping" .

There are a number of good books published on alarm management. Make a start by getting a copy of the ISA document 18-2. It has some very good guidelines.

Have never come across alarm settings on a P & ID. Could be a good idea. I insist that any alarm changes are reviewed by a qualified committee who meet weekly. 3 Mile Island was not an alarm issue but failure of the system to correctly indicate the position of the pressure relief valve, which I suppose could have created an out of position alarm.

I think back to when we moved away from the conventional control panels to the modern HMI graphics. We made so many mistakes. We took away pattern recognition, we used red and green for motor states when 3 out of 10 operators have red/green colour recognition problems, and now, I'm having to fight the IT department who consider themselves qualified to getting into the process control world. Isn't this new technology great?

On a lighter note we thought we could introduce voice recognition for plant control. Operator would read a paragraph so the system knew he/she was on shift. Then they could control with voice commands. Unfortunately some of them stutter.

__________________
Allan Evans
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #11

Re: An Alarm for Each PID Controller in DCS

10/19/2012 5:13 AM

<...never come across alarm settings on a P & ID...>

Likewise. The settings need to be stated on a separate Alarm Schedule document. Then, should an alarm need changing, the Alarm Schedule can be changed post HazOp study for the need for the change, which is easier to do than altering the P&ID.

A situation where programmers have to use their initiative rather than work in response to approved design documents is a 3-Mile-Island waiting to happen. However, it also exposes weakness in the testing regime, which is a major component of commissioning; it is not possible to correctly commission a plant where the design intent is inadequately stated beforehand - all one can do in these circumstances is turn it on and hope for the best!

Needless to say, a document control system needs to be in place at each facility to make sure all changes of intent and records of test are correctly documented.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Allan Evans (1); bigg (1); JPV (1); karthik301 (1); ozzb (1); Phys (1); PWSlack (4); thong (1); vargaalex (1)