Transformer Earth Shield

09/27/2012 11:46 PM

I bought a three winding transformer. If we are talking about secondary side, what is the difference between adopting "one foil" or "two foil" in terms of earth shield? On two foil, what would be the difference if the earth shield is connected together or not?

Thanks in advance.

Register to Reply
Pathfinder Tags: Transformer Earth Shield
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Transformer Earth Shield

09/27/2012 11:59 PM

How tiny is this transformer?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#2

Re: Transformer Earth Shield

09/28/2012 12:03 AM

Sorry.... It's a 3 MVA, 11/1.7/1.7 kV, Dyd

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Transformer Earth Shield

09/28/2012 12:36 AM

And it's wired with foil-shielded cable?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#4
In reply to #3

Re: Transformer Earth Shield

09/28/2012 2:12 AM

Yes

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5

Re: Transformer Earth Shield

09/28/2012 7:44 AM

Your transformer is D y D = delta / star+delta.

First, Shield is used to take out the 3rd harmonics currents from the system.

3rd harmonics will be eliminated in Star winding with shield.

Delta winding does not require shield to nullify the harmonics.

In your specific case, if two shields are joined internally, & brought out & separate earth given to shield, in my opinion, effect will be same as explained above. No harm.

__________________
Exploring the Science of Electricity
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#6
In reply to #5

Re: Transformer Earth Shield

09/28/2012 8:14 PM

Thanks Potter, but if you said the Delta winding does not require shield, then it should be only one shield in the transformer? Because they specifically said they provide two shield in the secondary.

And what is the difference if the connect the shield together and earth it or earth them separately?

Register to Reply
2
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#8
In reply to #6

Re: Transformer Earth Shield

09/29/2012 3:35 PM

"And what is the difference if the connect the shield together and earth it or earth them separately?"


If the shields are connected together before earthing, differing ground loops is negated. If the shields are separately earthed, the windings may sit on different ground planes causing ground loops and therefore equipotential is not assured.. Having the winding shielded then earthed also minimized the electrical leakage currents of the transformer.

__________________
vsar
Register to Reply Good Answer (Score 2)
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#7

Re: Transformer Earth Shield

09/29/2012 5:52 AM

According my opinion, a shield is a kind of cupper foil that is placed between the windings.

A connection lead to the shield is brought outside the transformer.

Is it not possible that the shields are used for

1) to minimise the capacitive coupling between the two winding placed aside?

the higher harmonic currents will flow between the winding and the shield and will not affect the other winding.

2) in case of a break down of the transformer, there will be no electrical connection between primary and secondary winding. There will always be a short cut to earth.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

harry potter (1); Local_Eng (3); rudy.leurs (1); Tornado (2); vsar (1)

Previous in Forum: Reversing Polarity   Next in Forum: AC to DC

Advertisement