During the secondary injection testing of siemens 630A ACA with rated overload set at 252A, a current of 350A was applied to the a.c.b through cables of 35 mm2 p.v.c . however with passage of time the injected current decreased from 350A to 335A .the a.c.b then tripped at 335A after 170sec while i applied initially 350A. why this automatic reduction of injected current.
India - Member - New Member
Good Answers: 164
Re: Current injection
10/02/2012 5:41 PM
Er,,when you say 'secondary injection', you must mean that you are passing a current through the relay which is normally done by the seconday of the CT...yes? If so, that current is likely to be a percentage of 5A usually, if the CT has a X/5 ratio. When you say 350A, do you mean that you have multiplied the actual current passed by the ratio?
OK, assuming you have done that, has your source sufficient power to drive the current through the relay? Is there a heater in the circuit which increases in resistance as it heats up (quite normal in bimetallic elements) thereby reducing the current flowing through it?
Good Answers: 34
10/02/2012 9:18 PM
One or more than one cable joints have unacceptable levels of resistance.
Good Answers: 164
10/02/2012 9:26 PM
Possible, even likely.
But then, why does the current drop after some time? Could be aggravation of the loose contact, or risng resistance somewhere, maybe even internal to a weak source.
10/02/2012 11:36 PM
The heating of the windings will increase their resistance, causing a decrease in current drawn. I don't know if this effect is enough to account for the reported decrease.
10/03/2012 12:20 AM
I meant to say wiring (etc.) rather than windings, but it became too late to edit.
10/03/2012 12:16 AM
What is the rated current of the CB,what do you mean by 630A ACA?. Why did you set OL at 252A and why you injected 350A in the primary?. What is the CT ratio?.
pnaban
10/03/2012 5:13 PM
Well ,i figured out that problem was in the cables i.e the 35mm2 cables from injector to a.c.b which overheated extreemly at such high current .so i used larger leads of 95mm2 and problem was solved.just sharing my experience.
Good Answers: 164
10/03/2012 8:44 PM
Ahh..so you mean PRIMARY injection, don't you?