10/11/2012 4:31 AM
pls tell me the specification of this cable size , 6*3.5c*300 mmsq
Re: cable size
10/11/2012 5:06 AM
It is not possible from the description given.
Re: cable size
10/11/2012 5:17 AM
no sir,it is there,our consultant provide me this size for the main cable from generator to MDP.The full specification is 6 * 3.5c * 350 mm.sq (XLPE / pvc) + 1c * 300 mm.sq PVC (G/Y).I understand 3.5c * 350 mm.sq,but i dont know what is this 6 for ?
Re: cable size
10/11/2012 5:33 AM
Ah! That's the specification!
See #3↓.
Good Answers: 34
Re: cable size
10/11/2012 1:30 PM
How many generators are connected to MDP? What is the out put of the generator?
Re: cable size
10/11/2012 1:59 PM
Two generators of 1000 kva each.
Good Answers: 34
Re: cable size
10/11/2012 3:03 PM
In your Main Distribution Panel, is there provision to connect, six numbers of 3.5c X 300 mm2 cables? Do you get the drift of the hint?
Good Answers: 181
Re: cable size
10/11/2012 5:31 AM
6 cables in parallel? Ask the consultant.
Re: cable size
10/11/2012 6:23 AM
May be the spec is like 6 X 3.5C X 300mm2 . if , it is , then normally it is treated like 6 runs of 3.5 core 300mm2 cable. But , then again , you can always ask ur consultant .
Re: cable size
10/11/2012 6:56 AM
Yes ofcourse,it is 6 x 3.5c x 300 mm.sq.But once again what is meant by 6 runs,because there is one more cable with 8 x 3.5c x 300 mm.sq size.
Re: cable size
10/11/2012 7:08 AM
The number of runs is the number of discrete cables of the specified type configured in parallel. Don't take this thread's word for it, though. Telephone the consultant instead.
Re: cable size
10/11/2012 7:15 AM
The single cable is a grounding cable; note the G/Y color. The other six cables are in parallel; each of the them has three line conductors plus a smaller sized neutral.
Re: cable size
10/11/2012 8:32 AM
Why not ask your consultant?
Re: Cable Size
10/13/2012 1:22 PM
It is a bunch of 6 cables, each cable has a cross-sectional area of 3.5mm2.The overall cross sectional area of the cable bunch is 300mm2
The actual current carrying capacity of the CABLE CAN ONLY be determined from MANUFACTURER'S TABLES.
Note that the current rating will depend very much on the AMBIENT TEMPERATURE of your locality.
Re: Cable Size
11/12/2012 11:39 AM
I think it mean 6 bundle of 3C+PE cable which have 3Cx300 sq.mm. + PE 150 sq.mm.