Generator 3 Phase 4 Wire and Delta-Wye Transformer

10/14/2012 11:46 PM

Generator 400/230 VAC 3 phase 4 wire. Can it connect to delta-wye step up transformer ? How about the vector group of transformer ? and star point of the generator could be connected to ground or not.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Generator 3 phase 4 wire and delta-wye transformer

10/15/2012 3:10 AM

A1) Yes, it can.

A2) OK, what about it?

A3) Follow the wiring codes applicable to the country of installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#2
In reply to #1

Re: Generator 3 phase 4 wire and delta-wye transformer

10/16/2012 2:11 AM

Very good, but if you are wiring delta-wye, why would you? The ground/neutral will be provided on the wye side.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#3

Re: Generator 3 Phase 4 Wire and Delta-Wye Transformer

10/16/2012 8:30 AM

You can connect the Generator 3 phases to the Delta side of the transformer, provided the voltage rating is correct.

You can connect the Star point of the genset to ground. It will serve to trigger any protection device on the Gen side with the primary delta winding.

The vector group of the Transformer is stamped on the nameplate and remains the same while having nothing to do with connecting the Generator (Unless you are parallelling the transformer ...

The secondary winding, Wye, will have a central point, the Neutral, which can be connected to ground to allow the proper functioning of protective devices downstream of that 2ndary winding.

Register to Reply Score 1 for Good Answer