what is cable termination torque?
how much needed?
how can we measure the cable termination torque?
Pathfinder Tags: cable termination torque
Re: cable termination torque
10/15/2012 7:49 AM
A3) With a torque wrench.
10/15/2012 7:50 AM
can u give me defn of cable termination torque?
10/15/2012 7:52 AM
No. The only answer available fitted the third question only.
10/15/2012 7:57 AM
weather should we maintain higher torque for high voltage cable?
10/15/2012 8:07 AM
Telephone calls to both the cable supplier and the termination component supplier would answer the query.
Good Answers: 804
10/15/2012 12:05 PM
It is usually the termination device that detarmines the torque value.
10/16/2012 4:05 AM
Useful to know.
10/15/2012 7:08 PM
No, you follow the instructions relating to the specific joint (the torque varies) as too much or too little torque is bad.
You are a student aren't you, because based on your questions I would be very concerned if you actually work in the power industry?
Re: Cable Termination Torque
10/15/2012 11:12 PM
Cable termination torque is often specified by the mfr of the cable termination device. Small ones can be done with a torque screwdriver, larger ones with a torque wrench.
Good Answers: 42
10/16/2012 7:30 AM
The answer the first part of the question is already there in your question.
How much needed depepend on the type of rermination
Measuring the termination torque by a torque wrench
10/17/2012 4:23 AM
At the time of cable termination the cable lugs to be tightened(ie torqued) as per the manufacturer recommendation. The termination torque may vary with bus bars, cable size etc. The manufacturer should specify a terminaation torque. Torque wrench is used for the measurment of torque