Power Line Tripping

10/16/2012 3:59 AM

Is unbalanced load in MV lines will cause tripping of earth fault relays in the feeder protection?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Power line tripping

10/16/2012 4:00 AM

No. Only an earth fault will trip an earth fault device.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Power Line Tripping

10/18/2012 9:35 AM

Yes! If the unbalance current is more than the setting made in the earth fault relay.

Register to Reply
Member

Join Date: Oct 2012
Posts: 5
#3
In reply to #2

Re: Power Line Tripping

10/19/2012 8:49 AM

Recently I read in an article which explains as below;

"A common misconception is that zero-sequence current only exists under fault conditions.

However, zero-sequence current can and does exist under nonfault, normal load conditions.

Unbalanced system conditions, such as those caused by nontransposed transmission lines or

unbalanced loading, can cause zero-sequence current to flow. Ground fault protection elements should never be set more sensitive than the normal system unbalance. This setting limitation means that load or system induced zero-sequence current can severely impact the sensitivity of a zero-sequence overcurrent element".

Do you agree on the above statement?.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Power Line Tripping

10/19/2012 10:37 AM

Yes! I very much agree with the statement.

Register to Reply
Member

Join Date: Oct 2012
Posts: 5
#5
In reply to #4

Re: Power Line Tripping

10/19/2012 11:36 AM

Consider following scenario in a 11kv feeder equipped with normal over current and earth fault protection relays.

The feeder tripped on overcurrent due to a short circuit and one phase jumper opened.But after test charge the line hold?

This is a major unbalance in the feeder?Can you please explain your view in this case?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Power Line Tripping

10/19/2012 12:06 PM

Information insufficient to opine.