10/16/2012 3:59 AM
Is unbalanced load in MV lines will cause tripping of earth fault relays in the feeder protection?
Re: Power line tripping
10/16/2012 4:00 AM
No. Only an earth fault will trip an earth fault device.
Good Answers: 170
Re: Power Line Tripping
10/18/2012 9:35 AM
Yes! If the unbalance current is more than the setting made in the earth fault relay.
10/19/2012 8:49 AM
Recently I read in an article which explains as below;
"A common misconception is that zero-sequence current only exists under fault conditions.
However, zero-sequence current can and does exist under nonfault, normal load conditions.
Unbalanced system conditions, such as those caused by nontransposed transmission lines or
unbalanced loading, can cause zero-sequence current to flow. Ground fault protection elements should never be set more sensitive than the normal system unbalance. This setting limitation means that load or system induced zero-sequence current can severely impact the sensitivity of a zero-sequence overcurrent element".
Do you agree on the above statement?.
Good Answers: 170
10/19/2012 10:37 AM
Yes! I very much agree with the statement.
10/19/2012 11:36 AM
Consider following scenario in a 11kv feeder equipped with normal over current and earth fault protection relays.
The feeder tripped on overcurrent due to a short circuit and one phase jumper opened.But after test charge the line hold?
This is a major unbalance in the feeder?Can you please explain your view in this case?
Good Answers: 170
10/19/2012 12:06 PM
Information insufficient to opine.