Submersible Pump

10/16/2012 3:54 AM

We have a star delta control panel for controling five 7.5 kw motors but unfortunately the motor is submersible type and it is delta connected type. how can we connect this panel to the motor. Any new addition needed for this.

please help me to solve this problem

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: submersible pump

10/16/2012 3:59 AM

The compartment for the motor that is delta-only needs to be redesigned and rebuilt as a direct-on-line starter. This is not a job for the uninformed, so the best thing to do is to contact a specialised local panel-builder that can come to site, do the drawings and carry out the alterations. Yellow Pages?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Oct 2011
Posts: 95
#2

Re: submersible pump

10/16/2012 6:22 AM

DOL, auto transformer or soft start are the solutions for 3 lead motors. star delta starters are used with 6 lead motors. but i am not sure about your system voltage .

Reply
Anonymous Poster #2
#3

Re: submersible pump

10/16/2012 7:04 AM

dear,

You will have to do few modifications in panel, so that motor can be run in direct on line. and if u want to reduce starting current then auto transformer or soft starter may be used.

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: Submersible Pump

10/17/2012 4:39 AM

You could remove the cover of the pump terminal box. If there are 6 terminals (connected in delta) you're in with a chance. Check out the cable needed for star/delta (probably 7 cores, including earth). If the existing cable gland will take the new cable, you're OK. Just possible there is a spare gland, blanked off. If so, it's easier, you can run a 2nd cable.

Obviously you need a star/delta starter, and wire it all up properly.

__________________
Give masochists a fair crack of the whip
Reply