Previous in Forum: Current Measurement in VFD   Next in Forum: How to Select the PMG for the Synchronous Generator ?
Motor mccb Design
10/16/2012 7:24 AM
how to design the mccb for motor. is it 2.5 times the full load current
Re: Motor mccb Design
10/16/2012 8:43 AM
The correct way is to follow national electrical design and installation standards. In the UK, British Standard 7671 gives full protocol on co-ordination between circuit protective devices, cables and motor overloads.
The circuit protective device looks after the cables. The motor overload device looks after the motor. Co-ordination ensures both are correctly selected. So it would be wrong, in principle, to use the mccb to try to protect against overload as it cannot do this, and motor failures will ensue.
10/16/2012 11:40 PM
Try motor circuit breaker.You should select not design.
pnaban
France - Member - New Member
10/17/2012 2:48 AM
Good Answers: 170
10/18/2012 9:32 AM
Pl. inform me your mail ID thro this forum's mailbox so that I can send you a technical paper on the subject. It is too large to be posted here directly.
Register to Reply 4 comments