Instrument Cable Meggering

10/16/2012 9:57 AM

gents, can u tell me the formula for insulation test? That how much mega ohms will get when we giv 500v.. ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: instrument cable meggering

10/16/2012 10:01 AM

Most Clients in industry don't ask for instrument cables to be tested at 500V as this far exceeds any voltage they might see in use. A continuity test is usually all that is required.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#2

Re: Instrument Cable Meggering

10/16/2012 12:09 PM

There is not such a thing as an equivalence between mega ohms and applied voltage.

The resistance measured is a result of dielectric specs, thickness, air gap, porosity, defects and area of the insulator as well as area and shape of the conductors on the sides.

The IR (insulation resitance) tests apply a voltage high enough (500V is very common) to reveal any leakages due to defects in the insulation materials of electrical equipment.

It is a safety test that is non-destructive, as opposed to Hi-Pot, which deteriorates the insulators with every test.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Score 1 for Good Answer