Temperature Control Valve

10/16/2012 4:25 PM

I know a salesman showed me a pneumatic valve positioner with an integral temperature controller. (you feed in a RTD input and plant air and the valve positioner will function as a temperature controller and I/P positioner with no other external circuitry and allow set points/PID cotrol/etc. as well as display the temperature) I can't remember who makes it. I checked Fisher and Schubert & Salzer which we usually use and it isn't either of those companies. I tried Googling, but apparently haven't hit the correct combination of terms to find it. Loads of I/P type control valves and TIC panel meters come up.

The real final goal of this is a TIC and positioned globe valve for steam control to a heat exchanger in a Class I Div.1 atmosphere. I was hoping the integral device mentioned above would eliminate one more exp rated box and set of seals.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Temperature Control Valve

10/16/2012 5:49 PM

Festo do a lot of that kind of stuff. Worth a try.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: Temperature Control Valve

10/16/2012 7:29 PM

I don't know about RTD sensors and I/P's on the valve, but self contained, capillary bulb temperature regulating valves have been around for a century or so.

http://www.jordanvalve.com/products/regulators/temperature

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#3
In reply to #2

Re: Temperature Control Valve

10/17/2012 8:40 AM

Exactly - about a century old (bio-tech customer isn't going to be thrilled with this) and definitely missing the "I" as in "indicating". Need a T read out too.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#5
In reply to #3

Re: Temperature Control Valve

10/17/2012 9:26 AM

Here's the missing 'I'. Install one in a thermowell.

Seriously, how are you going to get from a resistance input (RTD) to a pneumatic output, with no other connections? There's no electrical power source (unless it's battery powered or uses an air-driven micro-turbine generator or something).

Here's a link to an RTD in, 4-20mA out temperature controller, but it requires loop power and the documentation is sparse:http://senseinstruments.en.alibaba.com/product/278563480-202921044/temperature_controller_199A.html

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#6
In reply to #5

Re: Temperature Control Valve

10/17/2012 9:43 AM

You mis-read the question - the device I am looking for, and I have seen it, looks like a standard valve mounted I/P, such as Fisher's DVC6200 with a TIC similar to a Red Lion T16, mounted in the same instrument case. No need for 2 devices, as both are built into one case. LED display/programmable PID curve/RTD to 4-20ma conversion/I to P all in one housing. Some ingenious company realized that almost all TCV valves need a TIC to run them - so why not put them together in one housing. The thing I don't remember is if it is NEMA 7. If it isn't I will still need the two devices. I know where to get the NEMA 7 I/P and can put the TIC in my main NEMA 7 box for the other control items with a window for the display. Just trying to simplify the wiring a bit.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#7
In reply to #6

Re: Temperature Control Valve

10/17/2012 11:36 AM

OK. Must have been Leslie PMC-2. It doesn't appear to be NEMA 7. Here's a link:

http://www.lesliecontrols.com/catalogindex/PMC_2Page.pdf

Unless you need remote set-point or remote temperature indication, I don't see why you're avoiding the non-electric route. Must be one of those young pups I keep hearing about . Here's a link to a pneumatic TIC (this one has the indicator built in):

http://www.bbinstruments.com/downloads/Model_40.pdf

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#8
In reply to #7

Re: Temperature Control Valve

10/17/2012 11:55 AM

Yeah - that's the idea, but it is only NEMA 4. May use this on other skids.

Young pup? The first go round at higher education, I studied tubes in college - transisitors were a new novelty. The pharma / bio-tech industry hasn't used pneumatic controls in several decades and I am hesitant to suggest it to them. (however we are looking at a wind up temperature recorder right now for them) Last time I suggested Spirax/Sarco's capillary controlled valve for steam to a heat exchanger I got a very big NO.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#4

Re: Temperature Control Valve

10/17/2012 8:40 AM

Not too good at keeping cards - drag them home and my wife always file 13's them.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (2); Iris (1); JohnDG (1); Phys (4)

Previous in Forum: Control Valve Positioning   Next in Forum: Oven Controller with Set Point Output

Advertisement