Hello,
I am looking for an oven controller that outputs its set point or from which the set point can be read. Our current controllers are Watlow 93s or similar.
We have several ovens that have their set points changed constantly as needed for different jobs. We also regularly bake parts at the wrong temperature because folks get in a hurry and do not check the set point before putting their parts in the oven.
We are thinking that we would like to have a temperature verification system that gives instant feedback about whether the temperature required matches the set point of the oven.
Our current thinking is to print a barcode on the job traveler that has the required bake temperature. Scan the traveler at the oven. Compare the scan to the set point and flash a red/green light as appropriate. We need to be able to easily change the set point of the oven when required.
I would like to keep this as simple as possible, but can see it escalating quickly when QA gets wind of it and requires verification that the check was done, integration to plant software, etc., ad nauseum.
Any guidance/ideas/alternate approaches will be greatly appreciated,
Mike W.
You have to actively participate in the manifestations of your own joys and good fortunes - they are not ready made for the taking, they are available for the making.
Pathfinder Tags: barcode controller
Re: Oven controller with set point output
10/17/2012 2:41 PM
The Watlow, is a pretty reasonable cheap device.
For a temperature verification, you'll need some more control, with an RTD and possible a displat screen.
Its pretty hard to program out sloopy/lazy operators though.
Good Answers: 104
10/17/2012 2:43 PM
It looks like the Watlow F4 has the capability to retransmit the setpoint and/or process variable as 0-10V or 4-20mA. You might need both to make sure your oven has actually reached the setpoint - or use a deviation output alarm point. You didn't mention your controller output requirement, so you'd have to check that. Obviously, there are many other ways of accomplishing this - PLC, etc.
As far as keeping it simple, I think you're past that point . I see a database of temp vs barcode being needed, and if this info already exists somewhere else, you'll need to access that, otherwise the two will be out of sync before you know it, and who gets the blame then?
Re: Oven Controller with Set Point Output
10/18/2012 3:28 AM
Is there a way of reorganising the workflow such that a batch or a campaign of items are baked at one temperature before the oven is reconfigured for a different batch or campaign, rather than have the temperature setting dance about all over the place?
Just askin'.
10/18/2012 10:16 AM
We are a job shop, so work flows through as it arrives. Our method of organization is having a few ovens that run at the same temp all the time and the rest that are reset as needed.
Mike W.
Good Answers: 104
10/18/2012 1:57 PM
Here's how I envision accomplishing your task. You would need:
A. Temperature Controller with retransmit capability of Setpoint and Process Temp. (maybe Watlow F4, as mentioned earlier)
B. Central Processor, could be PC, PLC, etc, with:
Inputs: 1. Barcode reader, 2. Setpoint (SP, from Controller), 3. Actual Oven Temp (PV, from Controller)
Outputs: 1. Not ready light (or oven door lock), 2. Ready light (or unlock the door)
C. Program 1. Turn Not Ready light on, 2. Product detected (by barcode scanner), 3. Read barcode, 4. Get required temp (RT) from RT vs barcode table, 5. Get Controller Setpoint (SP), 6. Compare SP to RT [If <>, go to 1.], 7. Compare |PV - SP|< tolerance for enough time for oven to stabilize, 8. Turn Ready light on and set timer to give operator time to load furnace, 9. Go to 1.
Obviously, this is rudimentary. For example, time could be saved if the oven 'soak' time was continuously monitored so the wait interval could be eliminated if the oven had previously been at the RT.
New Zealand - Member - Member Australia - Member - Member
Good Answers: 43
10/18/2012 7:40 AM
These Watlow models, like most controllers (TOHO, Shinko) display the setpoint as well as the process value. Is this suitable ?
10/18/2012 10:21 AM
I need the controller to output the setpoint, not just display it. The Watlow 93s that we use now display the set point, but we still get the occasional error.
I need to have two things to compare: What the set point is, and what the set point should be.
Thanks,
Mike W.
10/18/2012 10:41 AM
A signal or recorder?
10/18/2012 10:44 AM
I need a signal, because I want to compare it to the required set point for the job.
Thanks,
Mike W.
Good Answers: 43
10/18/2012 7:32 PM
Does the Watlow coms software provide a solution ?
http://www.watlow.com/products/controllers/specview-hmi-software.cfm
10/19/2012 10:49 AM
It has great potential.
Thanks,