Load Balancing in a Three-Phase System

10/18/2012 8:36 AM

What is the advantage of balancing a three-Phase System with single-phase loads connected to phase A, B, & C in a commercial building? Is the existing unbalance currents in three phase can affect power consumption of the building? Ia=180A, Ib=120A & Ic=200A. Can balancing efforts will reduce our present monthly power billings? Pls. help!

Register to Reply
Pathfinder Tags: Load balancing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Load Balancing in a Three-Phase System

10/18/2012 9:01 AM

Generally, the capacity of a feeder is limited by the upstream circuit protective device's trip setting. In the example given, say the setting were 200A for instance. Any attempt to add additional load to C would therefore cause the trip to operate, whereas there is some capacity left on A and quite a bit more on B. So in this case, one might be tempted to add any additional single-phase load to B first.

Balancing the load to an average of 167A on each phase in this case gives capacity to add more load to any of them with little consequence. Start by taking single phase loads off C and moving them to B first.

And no, balancing the single phase loads will not affect the billings much at all.

However, if the facility is being charged for low power factor, an assessment might be worthwhile to see if spreading individual loads aroung individual phases might help. PF correction is done in an economic environment; the investment may not be worthwhile at all, and is certainly a non-starter if there is no low-PF charge component in the supplier's energy tariff.

Remember to invoke energy conservation measures before making any investment in PF correction, as the payback time is usually far shorter!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 4)
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#4
In reply to #1

Re: Load Balancing in a Three-Phase System

10/18/2012 10:47 PM

Thanks for your practical technical info. we presently monitor each phase line current.Hope we can start to transfer some of the loads to A & B. Maybe, we need to identify first the non & contin. loads. God bless.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #4

Re: Load Balancing in a Three-Phase System

10/19/2012 3:19 AM

There will always be some imbalance as, by their very nature, single phase loads are usually of an intermittent and variable nature.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Load Balancing in a Three-Phase System

10/18/2012 11:09 AM

Another possible consequence is with regard to any 3 phase motors you may have, such as for air handling equipment. A severe current imbalance will create a voltage imbalance. A voltage imbalance in a 3 phase motor will cause it to heat up a lot more than it should. This is not only going to severely shorten the motor life, but that heating represents a waste of energy, so that can affect your building energy use.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Load Balancing in a Three-Phase System

10/18/2012 11:23 AM

Good point. GA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#5
In reply to #2

Re: Load Balancing in a Three-Phase System

10/18/2012 10:52 PM

Mr. Guru, we experienced frequent trippings in our 3 Phase elevator motors. Thank you.

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: Load Balancing in a Three-Phase System

10/18/2012 11:20 PM

I have a basic agreement wit all said before. But, think for a moment. If one phase is 300 Amps, the other is 100Amps, which will burn out first?!?

Your good guess will earn browny points.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#7

Re: Load Balancing in a Three-Phase System

10/18/2012 11:59 PM

In case of Y connected secondary with the star point earthed i.e in a three phase four wire system, the high unbalance current in the three phases will increase the neutral current. Ideally if IA= IB = IC then the vector sum of all the phase currents will be zero, hence neutral current will be zero. High unbalance current may cause heating of the neutral conductor if the size of the neutral conductor is half the size of the phase conductor.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#9

Re: Load Balancing in a Three-Phase System

10/19/2012 3:32 AM
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#10

Re: Load Balancing in a Three-Phase System

10/19/2012 3:47 AM

Ideally you want to try and balance out the loads. When juggling single phase loads at best you can get close. In a building a hot air hand dryer or local zip boiler can throw the loads around and imbalance the system.

The generating station likes a nice even load - it smooths out the mechanical imbalances on the generating machines.

As for billing its unlikely affect it.

Be aware of the need to monitor and if neccessary increase the size of the neutral in a TP&N cable if there are lots of single phase loads around and I'm thinking here single phase loads with the ability to introduce harmonics.

The supply authority has a remit to supply within certain tolerances so I can't see over running a motor being an issue.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#11

Re: Load Balancing in a Three-Phase System

11/04/2012 6:11 AM

I would like to view the problem from the point of view of the generating equipment namely the generator. Each generator has limited capability of supplying the unbalanced load. This is known as I2squared t (sorry I could not write 2 as subscript of I). Here I2 is negative sequence current and t is the time for which is I 2 could be permitted. Any unbalanced load can be considered to be made of three components, positive sequence, negative sequence and zero sequence. The negative sequence current produces magnetic field which revolves at synchronous speed but in reverse direction to that produced by positive sequence (balanced) load. So the relative speed between magnetic field created by the negative sequence and the rotor is twice the synchronous speed. This results in induction of double frequency voltage and the resulting current in the rotor body which is normally not designed to carry such current. So the rotor gets heated and may get damaged if such current is allowed to pass. The rotor has inverse time characteristics for with standing this current. To protect the generators from negative sequence current, protection relays (negative sequence protection relay) are provided. So many power providing companies impose a penalty for unbalanced loads on bulk consumers. I as a generator designer, would request each consumer to understand the effect of unbalanced load and try to minimize the unbalance load.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); JRaef (1); leveles (1); nobodysomebody47 (1); pcchatur (1); PWSlack (3); siegfredo c. tabanag (2); silverfox (1)