Kindly advice That one of my Transformer 11Kv / 415 V - ( 1500KVA ) - earth resistance valve showing 10.67 ohms . please tell me that what are reason earth resistance will go high and what to be done to take down the valve.
Good Answers: 34
Re: Transformer 11Kv - high resistance Valve
10/18/2012 6:22 AM
Power down the transformer, check all joints on the earth conductor, for corrosion & poor contacts.
10/18/2012 7:22 AM
...then find all the earth rods and matting, and empty a road tanker full of seawater onto each one. If seawater is unavailable, cow urine makes a tolerable substitute.
Re: Transformer 11Kv - High Resistance Valve
10/18/2012 4:13 PM
... and if you're short of cows, get all your friends together ...
10/18/2012 4:15 PM
What was it before, and what has changed on or near the transformer site since the last and current measurements?
10/19/2012 1:30 AM
What type of earth rod is used,howmany years ago it was installed,did you measure the resistivity of the soil,were periodic readings taken,try earth enhancing material.