Motor Fault

10/23/2012 1:51 PM

Hi all

WE have a motor that triped with overload, I decoupled the compressor from the motor and started it up.

Within a few seconds a fuse blew, I meggered the motor winding and found all ok. Replaced the fuse and restarted it, this time 2 fuses burnt out, and I noticed that while the motor free wheeled to a stop that the direction of rotation was incorrect... I find this strange .. as the compressor has been in service for about two years.. could a faulty contactor cause a motor to loose a phase causing it to rotate in a different direction and then blow two fuses ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Motor Fault

10/23/2012 2:05 PM

Most likely is the cause. You can easily investigate. Power down at DB. Measure resistance across contacts with contactor manually engaged. It should be zero. Alternate method, tag & remove all terminals from motor. Power up & measure voltage put out from contactor. It should be same as your normal motor supply.

Register to Reply
Commentator

Join Date: Sep 2009
Posts: 72
#2

Re: Motor Fault

10/23/2012 3:00 PM

Heres where I begin to have doubts about the contactor being faulty... I opened it up to inspect the contacts and they have signs of wear, but not excessive... with power off I forced the contactor in and all the contacts are touching.. surely I would have a very vissible problem for example a missing contact or a badly worn contact with a vissible gap between contacts... (ps we are talking about a 200KW 400 Vac motor with a LC1 F400 contactor.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: Motor Fault

10/23/2012 3:35 PM

Look for short in the motor winding. You would need a Milli ohm meter.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#4
In reply to #3

Re: Motor Fault

10/23/2012 4:40 PM

Please do not power up the motor till the fault is conclusively located, proved & made good.

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Motor Fault

10/23/2012 5:01 PM
  1. NEVER replace only one fuse. When a fuse blows, it stresses the other fuses. By replacing only one, you all but guaratee that one of the others will blow sooner than later. If one fuse blows, ALWAYS replace all three. If you don't like that, specify circuit breakers.
  2. In the second incident, one of the two fuses likely blew immediately, creating a single phasing condition in which rotation (if any) is unpredictable. Then the 2nd fuse blew shortly thereafter.
  3. You may have a faulty motor lead. When you meggered the motor, did you do so at the motor peckerhead or at the leads in the motor starter. I always start by meggering the leads at the motor starter. If it's OK there, you are done. If it is not, THEN you check at the peckerhead. If it's not showing bad at the pecker head, you know it's in the leads and vice versa.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #5

Re: Motor Fault

10/24/2012 7:38 AM

GA

Good common sense.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#14
In reply to #5

Re: Motor Fault

10/24/2012 8:15 AM

GA JRaef!

I also agree with other posters who advise to switch off the power and check the resistance across the contacts of each phase of the contactor while closing the contactor manually. All three readings should be equal and indicate a low resistance. If the one reading obtained is unstable or different then this contact set would be suspect. Check also for free movement of the contactor as it closes - it is possible that dirt has infiltrated the contactor and is preventing it from closing properly providing equal contact pressure across each of the three sets of contacts.

The same goes for checking the winding's of the motor - not only test insulation between the winding's and also winding's to frame (earth/ground) but also measure the resistance of each winding.

Apart from the above please do not exclude a damaged rotor where one of the bars may be cracked. I use a very easy method to determine this but as the original poster has called the motor winders to site to test the motor they should be able to exclude this.

Re the motor changing direction - this would occur on any three phase motor that is 'single phasing' i.e. being supplied by only two of the three phases. I normally check this by spinning the motor shaft in one direction by hand and then starting the motor. Then after letting the motor coast to a stop, spinning the motor by hand in the opposite direction before starting the motor. If the motor runs in both directions then a 'single phase' condition exists.

Lastly, when a fuse blows it is because of an over-current problem and this should be cleared before replacing fuses. Fault finding is a process of looking until the fault is identified and unfortunately there are no shortcuts! Fault finding is a combination of technical knowledge, use of instruments, experience, thinking 'outside of the box', dealing only with facts and lastly patience!

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Participant

Join Date: Oct 2012
Location: Hilton Head Island, SC
Posts: 1
#17
In reply to #5

Re: Motor Fault

10/24/2012 10:29 AM

I have never heard the term peckerhead referred to as part of an electric motor. What is it?

I have been called a peckerhead when continually replacing fuses without finding out why they are blowing!

__________________
"I got my tan in Afghanistan" Alfred E Newman early 1960's
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#18
In reply to #17

Re: Motor Fault

10/24/2012 10:50 AM
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19
In reply to #17

Re: Motor Fault

10/24/2012 3:35 PM

To save time, I am copying and pasting something I wrote in another forum, replying to someone thinking my use of the term was not "politically correct" because of their mind being in the gutter...

  • Hey, there is no "political correctness" needed here! "Pecker Head" is a now commonly accepted term in much of the US for a motor termination box. As I learned long ago, the term was derived from "Picker Head" which was a protrusion off of a drum in old farm machinery which caught the material to be picked, be it an ear of corn, a sunflower head, a cucumber etc., and separated it from it's stalk or vine. Because the termination box on an electric motor looked very similar, it was called (probably) "that there picker head thang on the 'lectric motor"! Interestingly enough, in the South the term "Peckerhead" already meant a dullard and was also apparently derived from "Picker Head", but meaning someone too dumb to do anything on the farm but be a picker. With a Southern twang, "picker" can easilly end up sounding like "pecker".

    The non-PC meaning of either term likely came along a lot later.

    Hey what can I say. I did an etymology of common electrical terms once as a term paper for a class and the prof liked it so much he gave me extra credit to research oddball terminologies. I've forgotten most of them now but that one stuck because I later used it a lot.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#20
In reply to #19

Re: Motor Fault

10/24/2012 11:26 PM

No, it's because the usual slope of the motor junction box flange resembles the shape of the glans.

--Ed. C.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#21
In reply to #20

Re: Motor Fault

10/25/2012 8:04 PM

"No, it's because the usual slope of the motor junction box flange resembles the shape of the glans."

<Looks in pants>

Huh, doen't look like anything I've got down there...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#22
In reply to #21

Re: Motor Fault

10/26/2012 12:59 PM

Roundhead or Cavalier?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#23
In reply to #22

Re: Motor Fault

10/26/2012 4:00 PM

None of your GD business.

But I was born Cavalier, I know that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6

Re: Motor Fault

10/23/2012 6:26 PM

If the contactor is faulty (not your situation, but you asked) it is possible that one phase doesn't get any supply. But in such a case, the motor will not rotate, since this is what is referred to as a 'single-phasing' situation and there is no rotating field. The motor will draw a high current in the two phases, and the overload relay will usually trip, since the current will be in the overload region, not quite a short-circuit (which would blow the fuses). Perhaps the fuses are undersized, or have aged (not normal if they are from a reputed manufacturer).

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#7

Re: Motor Fault

10/24/2012 12:32 AM

Absolutley.

__________________
"Real Bass Players" do not use picks
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 72
#8

Re: Motor Fault

10/24/2012 1:05 AM

Thanks for your replies..

Just to clarify

I always replace the 3 fuses even if just one blows.. today I will replace the three contacts in the contactor just to remove any doubts.

I have a motor repair company comming out today just to verify the motor.

I meggered and supply cables at the contactor.

Thanks all

Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#9

Re: Motor Fault

10/24/2012 1:28 AM

Maybe we have to focus on why the rotation of the motor reversed! So there must be changes in phase sequence not single-phasing. Suggest to use phase sequence tester for both the line side and load side where terminals of the motor are temporarily disconnected.Sorry I cannot believe a possibility of interchanging of two phases inside the contactor.

Register to Reply
Active Contributor

Join Date: Sep 2009
Location: A.P., India
Posts: 20
#10

Re: Motor Fault

10/24/2012 2:38 AM

it seems that motor has an internal winding short-circuit. to find out you have to check both winding resistance & inductance. they must be equal for all 3 windings.

__________________
-- sitaram
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#12

Re: Motor Fault

10/24/2012 8:07 AM

you forgot to mention what kind of a starter you are using, where diagnosis will be more. But any way if the motor terminations winding continuity and insulation test readings are good and you have 3 phases in order the motor MUST run.In this case your insulation is good than it has to be motor windings / terminal fault or the starter contactor is not giving 3 phase, after all the load had already been decoupled.pls do confirm upstream voltages as well.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#15
In reply to #12

Re: Motor Fault

10/24/2012 8:23 AM

"you forgot to mention what kind of a starter you are using, where diagnosis will be more." First, please read post....

#2 we are talking about a 200KW 400 Vac motor with a LC1 F400 contactor.

#8 today I will replace the three contacts in the contactor just to remove any doubts.

Register to Reply
Commentator

Join Date: Sep 2009
Posts: 72
#13

Re: Motor Fault

10/24/2012 8:12 AM

Hi

Once again thanks for the replies...

Motor was tested (Inductance and Resistance) with a decent tester and not the normal fluke tester that we use.. one set of windings had a short circuit between the windings but not to earth.

Thanks all

Register to Reply
2
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#16
In reply to #13

Re: Motor Fault

10/24/2012 8:38 AM

Hi Porky 2009,

Thanks for coming back with the result of the testing! It's always good to know what happened.

Last thing here - the motor is probably on it's way to the winders to be rewound so please ask the winders to look and see where this winding short circuited i.e. in the slot, at the entrance to the slot, on the winding turns, winding burnt or just shorted? The position at which the damage occurred will be a pointer to why it occurred i.e. too frequent starting, overheating caused by fault on supply, loose windings etc. Once you identify the exact nature of the problem you will have a very good idea about how to prevent a further fault (or repeat performance!). Experienced winders have a good idea of exactly why a motor burnt out or failed.

Good luck!

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Good Answer (Score 2)
Member

Join Date: Nov 2011
Posts: 5
#24

Re: Motor Fault

10/27/2012 2:24 AM

In my opinion your rotor has broken bars in it. To verify connect a lower voltage (1/2 rated to two of the wires of the motor and put a clamp on ammeter on one line.Energize the supply and turn the shaft very slowly. The ammter wil go crazy when you are on the broken bars otherwise the reading will be steady. A rotor costs more that the entire motor so keep the peckerhead and throw the rest

Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (2); dougluba (1); Gord Graham (1); Jimh77 (1); Joshi (5); JRaef (4); Keith Grewar (2); kvsridhar (1); pillay (1); porky2009 (3); siegfredo c. tabanag (1); sitaram (1); Tornado (1)

Previous in Forum: Trafo Charging with DG Set   Next in Forum: Electrical Reference Collections

Advertisement