Urgent-Abt Busbar Sizing Calculation

11/07/2012 6:44 AM

Copper Bus bar sizing calculation including thermal withstanding capacity of bus bar under short circuit. help me which formula i can use to find the sizing with the above conditions.

for example take 3000A The i suggested is 1680 mm.sq

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: urgent-abt busbar sizing calculation

11/07/2012 7:25 AM

This topic is one of CR4's most-covered. Look.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Nov 2012
Posts: 4
#2
In reply to #1

Re: urgent-abt busbar sizing calculation

11/07/2012 8:50 AM

If a copper conductor conducts 4000 A at ambient temperature of 40 degree.and at 54 degree c.can i provide the same cross section of copper ? or am i want to go for higher rating?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: urgent-abt busbar sizing calculation

11/07/2012 9:11 AM

Do your own homework!

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: urgent-abt busbar sizing calculation

11/07/2012 9:40 AM

Why any organisation would direct someone to size a busbar without also giving that individual access to the design manual with which to size it correctly, thereby prompting that individual to ask anonymous strangers in a global engineering internet forum as a matter of urgency, is a thing of great wonder and abstrusion.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#5

Re: Urgent-Abt Busbar Sizing Calculation

11/07/2012 4:00 PM

Check this may help you

Busbar Sizing Calculation

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Urgent-Abt Busbar Sizing Calculation

11/08/2012 2:35 AM

Busbar cross section evaluation/calculation in two situations: short-circuit and continuous load. For short-circuit you have to state-at least-the clearing time.

For continuous load it depends on a few conditions as: natural or forced air circulation, the busbar geometry the enclosure shape and size. If the load will be

short time applied [or intermittent] will be another way to calculate it.

The maximum temperature it is dictated by the maximum temperature permitted for insulation-plastic, porcelain, silicon and so on.

As a rule of thumb the current for 54oC ambient air with respect of 40oC [let's say 85oC will be maximum permitted] sqrt((85-54)/(85-40))*4000=3320 A.

__________________
Julius
Register to Reply
Participant

Join Date: Nov 2012
Posts: 4
#7
In reply to #6

Re: Urgent-Abt Busbar Sizing Calculation

11/08/2012 8:35 AM

if suppose the maximum permitted limit is 105 means the calculation changes rit?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8
In reply to #7

Re: Urgent-Abt Busbar Sizing Calculation

11/08/2012 12:11 PM

Of course,the maximum permitted current will be then : sqrt((105-54)/(105-40))*4000=3543 A

__________________
Julius
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#9

Re: Urgent-Abt Busbar Sizing Calculation

11/09/2012 3:36 AM

As said already, busbar calculation simple formulas can only give rough results, which bring to a huge raw material overusage if we do not want to take risks.

Modern calculation softwares integrate conduction, convection, radiation, skin effect internal to one bar and induced by neighbouring phases, .... and allow to use up to half the cross section, with sophisticated shapes .. see http://www.youtube.com/watch?v=eHADHX-x85Y

Register to Reply
Participant

Join Date: Nov 2012
Posts: 4
#10
In reply to #9

Re: Urgent-Abt Busbar Sizing Calculation

01/06/2013 7:49 AM

have another doubt.our 1600 A busduct(720 mm copper flat ) is tested for 65 kA/1 Sec.i like to know how this 65 ka/sec is derived. please tell me the calculations

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); carrol (3); lyn (1); nobodysomebody47 (1); obouill (1); PWSlack (2)